RE: [EnergyPlus_Support] Water heater + condensing loop
Hi Miguel:
The loop pump running continuously will be taken care in the April release. Also while specifying operation schemes, specify lower limit of load as a value slightly above 0 (like 0.001), just to make sure it wont turn on any pump. however just this change will not solve the issue currently. In the April release this must be taken care of.
I believe the April release will have a new tempering valve object which will function as you mentioned
Currently you can simulate the Primary-secondary system using Plant connetion component. As Mike mentioned in a reply to another message, theorotically you canconnec t any number of loops but more that one loop is not tested.
Thanks
Sankar
S.K.Padhmanabhan
Research Associate
Mechanical & Aerospace Engineering
Oklahoma State University,
Stillwater, OK - 74075
Ph: (405)744-4380
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of Miguel Angel Pascual Buisan
Sent: Tue 3/7/2006 2:42 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Water heater + condensing loop
Thank you very much for your help.
We have followed your advice and now the model seems to be almost fine. We
have noticed again that the second loop pump is running continuously, under
no load on the "source side heat transfer" of the heatpump. I think that
this is the same issue I told you a few weeks ago.
I also think that the water heater is a smart object, but it would be better
if it could include a mixing valve in the output of the use side. This will
be very helpful for storing DHW at higher temperature than is served to the
hot water taps.
It will be also very useful for simulating a primary system with various
secondary loops with different flow rates and temperatures.
Miguel Ángel Pascual
Director Técnico
MIYABI espacios urbanos bioclimáticos
Leyre 11bis, 1ºC 31002 Pamplona
Tel: 948 20 36 44 Fax: 948 20 78 60
Email: <mailto:mapascual@xxxxxxxxx> mapascual@xxxxxxxxx
Web: <http://www.miyabi.es/> www.miyabi.es
_____
De: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de Padhmanabhan,
Sankar
Enviado el: lunes, 06 de marzo de 2006 19:40
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Asunto: RE: [EnergyPlus_Support] Water heater + condensing loop
Hi Miguel:
As you noted you cannot put a Water Heater:Mixed object in a condenser loop.
In EnergyPlus the components in condenser loop are generally Environmental
heat exchangers. However you can accomplish your objective by setting up two
plant loops as follows:
Plant Loop 1: Consists of Water-water HP in the supply side similar to the
way you would set up for a ground served system.
Plant Loop 2: In the demand side of the loop place the water-water HP and
the supply side must contain the water heater mixed. Make sure the nodes are
connected correctly. At this point note that the water heater mixed object
has 2 sets of inlet/outlet nodes viz. source side inlet and use side inlet.
In the above said configuration, the inlet nodes as seen from Plant Loop 2
to water heater must be the source side inlet. The use side nodes must be
the inlet/outlet nodes of the domestic hot water system you will specify.
Little while ago we did some testing on the water heater mixed object to see
how setting up two plant loops connected to each other work and from the
testing we noticed that the water heater mixed object is smart to take care
of such a situation. The above said method should work and we would like to
hear what your experiences are.
Thanks
Sankar
S.K.Padhmanabhan
Research Associate
Mechanical & Aerospace Engineering
Oklahoma State University,
Stillwater, OK - 74075
Ph: (405)744-4380
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of Miguel Angel Pascual
Buisan
Sent: Mon 3/6/2006 11:37 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Water heater + condensing loop
Hello,
We are working with a water to water heatpump condensed by vertical ground
heat exchanger. We want to estimate how much heat could be recover for
Domestic Hot Water use, so we replaced the ground exchanger with a "Water
heater:mixed" in the condensing loop. It did not work because it is not
possible to have this type of equipment in a condensing loop. Any idea about
how can we fix it?
Thanks in advance.
Miguel Ángel Pascual
Director Técnico
MIYABI espacios urbanos bioclimáticos
Leyre 11bis, 1ºC 31002 Pamplona
Tel: 948 20 36 44 Fax: 948 20 78 60
Email: mapascual@xxxxxxxxx
Web: www.miyabi.es <http://www.miyabi.es/>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
Yahoo! Groups Links
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
the "search" button.
SPONSORED LINKS
Email
<http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Email+softwar
e+program&w2=Cad+software+program&w3=Wedding+program+software&w4=Backup+soft
ware+program&w5=Medical+software+program&w6=Anti+virus+software+program&c=6&
s=176&.sig=WXY8cUmYWYoS2xp0ShWtkQ> software program
Cad
<http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Email+software+
program&w2=Cad+software+program&w3=Wedding+program+software&w4=Backup+softwa
re+program&w5=Medical+software+program&w6=Anti+virus+software+program&c=6&s=
176&.sig=A3b7SIMNdG1AjPavhace-A> software program
Wedding
<http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Email+softw
are+program&w2=Cad+software+program&w3=Wedding+program+software&w4=Backup+so
ftware+program&w5=Medical+software+program&w6=Anti+virus+software+program&c=
6&s=176&.sig=c3c1sWYfiWGzKp7GnUerLg> program software
Backup
<http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Email+softwa
re+program&w2=Cad+software+program&w3=Wedding+program+software&w4=Backup+sof
tware+program&w5=Medical+software+program&w6=Anti+virus+software+program&c=6
&s=176&.sig=J10TTRJ42b1D5Lkoj0m6lw> software program
Medical
<http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Email+softw
are+program&w2=Cad+software+program&w3=Wedding+program+software&w4=Backup+so
ftware+program&w5=Medical+software+program&w6=Anti+virus+software+program&c=
6&s=176&.sig=3tzE1foqgmqgLFq3H5bsSg> software program
Anti
<http://groups.yahoo.com/gads?t=ms&k=Anti+virus+software+program&w1=Email+so
ftware+program&w2=Cad+software+program&w3=Wedding+program+software&w4=Backup
+software+program&w5=Medical+software+program&w6=Anti+virus+software+program
&c=6&s=176&.sig=m6VVDXIwWlmoo53vppw1CQ> virus software program
_____
YAHOO! GROUPS LINKS
* Visit your group "EnergyPlus_Support
<http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
* Your use of Yahoo! Groups is subject to the Yahoo!
<http://docs.yahoo.com/info/terms/> Terms of Service.
_____
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/