RE: [EnergyPlus_Support] UFAD Unmet Load Hours Question
There are several issues at work here.
1. Some of the example files have a mismatch in the people schedules compared
to the HVAC thermostat schedules. We're working on cleaning these up, and I'm
not sure if these particular examples have been fixed yet. This may be part of
the reason for the "time not comfortable" hours.
2. The ASHRAE 55 comfort reporting is sensitive to zones which use displacment
ventilation and it uses an air temperature computed based on the comfort
specifications in the particular ROOMAIR MODEL specifications.
3. Are humidity conditions in proper control? The ASHRAE 55 comfort reporting
is impacted by both temperature and humidity.
4. The "setpoint not met" reporting, however appears to be using the Zone Mean
Air Temperature (based on a very quick look at the source code). I suspect
this should really be using the "thermostat" temperature as defined in the
particular room air model. I will submit a bug report on this (CR6926).
Thanks for bringing this to our attention.
Mike
On 20 Mar 2006 at 17:46, Justin Aruck wrote:
> Both the "Setpoints Not Met With Temperatures" report and the "Comfort
> Report" report.
>
> Justin
>
>
>
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Michael J.
> Witte
> Sent: Monday, March 20, 2006 5:21 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] UFAD Unmet Load Hours Question
>
> When you say "unmet cooling hours" what exact report or report variable
> are you
> referring to?
>
> Mike
>
>
> On 20 Mar 2006 at 17:08, Justin Aruck wrote:
>
> > Hello,
> >
> > I have been working on an underfloor air distribution model.
> Everything
> > seems to be running ok (airflows, sizing, and energy use are
> > reasonable), but I have lots of unmet cooling hours with the average
> > being only a degree or two off. I was curious and ran the example
> file
> > (5ZoneSupRetPlenVSATU) for a year and got around 1800 unmet cooling
> load
> > hours. Is there a reason for this, or are both my model and the
> example
> > not running correctly? I also had unmet cooling hours when running
> the
> > "Displacement_VAV" example.
> >
> > Thank You for any available guidance.
> >
> > Sincerely,
> >
> > Justin Aruck, LEED-AP
> > Sr. Energy Engineer
> > EMO Energy Solutions, LLC
> > 2733 Hartland Road
> > Falls Church, VA 22043
> > Phone: 703-205-0445 Fax: 703-205-0449
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the "search" button.
>
>
>
>
> SPONSORED LINKS
>
> Cad
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Cad+softwar
> e+program&w2=Medical+software+program&w3=Email+software+program&w4=Weddi
> ng+program+software&w5=Backup+software+program&w6=Anti+virus+software+pr
> ogram&c=6&s=176&.sig=YlE0nyOhr1_AN7NCV5fvQA> software program
> Medical
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Cad+sof
> tware+program&w2=Medical+software+program&w3=Email+software+program&w4=W
> edding+program+software&w5=Backup+software+program&w6=Anti+virus+softwar
> e+program&c=6&s=176&.sig=6qqgXMRVP4vQrB8ojDSI1Q> software program
> Email
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Cad+softw
> are+program&w2=Medical+software+program&w3=Email+software+program&w4=Wed
> ding+program+software&w5=Backup+software+program&w6=Anti+virus+software+
> program&c=6&s=176&.sig=JZkkPEghoDnge9wKvbrBNA> software program
>
> Wedding
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Cad+sof
> tware+program&w2=Medical+software+program&w3=Email+software+program&w4=W
> edding+program+software&w5=Backup+software+program&w6=Anti+virus+softwar
> e+program&c=6&s=176&.sig=zpF2JCt5rUQD0eJnlYGQBQ> program software
> Backup
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Cad+soft
> ware+program&w2=Medical+software+program&w3=Email+software+program&w4=We
> dding+program+software&w5=Backup+software+program&w6=Anti+virus+software
> +program&c=6&s=176&.sig=SJ_vr3FMQUeC11M0M1_E8A> software program
> Anti
> <http://groups.yahoo.com/gads?t=ms&k=Anti+virus+software+program&w1=Cad+
> software+program&w2=Medical+software+program&w3=Email+software+program&w
> 4=Wedding+program+software&w5=Backup+software+program&w6=Anti+virus+soft
> ware+program&c=6&s=176&.sig=DJ7neGect-hvz0rIL-GWlQ> virus software
> program
>
> _____
>
> YAHOO! GROUPS LINKS
>
> * Visit your group "EnergyPlus_Support
> <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
>
> * To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
> be>
>
> * Your use of Yahoo! Groups is subject to the Yahoo!
> <http://docs.yahoo.com/info/terms/> Terms of Service.
>
> _____
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/