Re: [EnergyPlus_Support] Differenct autosized value for the same component
The heat pump model actually has two heating coils. 1) the direct
expansion heating coil and 2) the supplemental heating coil. This model
is a little different than the "real" heat pump equipment. A heat pump
actually has a single coil that can heat and cool based on the position
of the reversing valve with a supplemental heating coil that is used in
case the direct expansion coil can not handle the load.. Since the
single coil in the heat pump can heat AND cool using a compressor, the
simulation model needs to simulate the "coil" as 2 separate "virtual"
coils with different performance characteristics for cooling and heating.
So the sizing info you see refers to the "virtual" DX heating coil (#1)
and the supplemental heating coil (#2) and sizing info for the cooling
coil (#3)). Why the heating coils are sized differently is another
question all together.
To add a second Window AC to a zone, add another exhaust and inlet node
to the zone and connect the 2nd Window AC to these nodes. Include the
Window AC in the zone equipment list to tell the simulation which one
you want to run first to meet the zone load. No examples exist since 2
small units are nearly the same as 1 larger unit.
eric_zhou1223 wrote:
> Hi,
>
> 1) When I ran the HeatPumpAuto.idf in the example files, I found
> that
> Supp heating coil seems to have two different autosized value in the
> eio file like below:
>
> Component Sizing, UNITARYSYSTEM:HEATPUMP:AIRTOAIR, DXAC HEAT PUMP 1,
> Supplemental heating coil capacity [W], 20848.
> ...
> Component Sizing, COIL:GAS:HEATING, HEAT PUMP DX SUPP HEATING COIL
> 1, Nominal Capacity of the Coil [W], 24821.
>
> Is that alright or I misunderstood something?
>
> 2)
> How can I put more than one set of WindAC into a single zone? Is
> exist a example file for a refference?
>
> Thank you
>
> Eric
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the "search" button.
>
>
>
>
> SPONSORED LINKS
> Medical software program
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Medical+software+program&w2=Email+software+program&w3=Backup+software+program&w4=Cad+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=MBRNFUVaa4AnhRZcL_SPpQ>
> Email software program
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Medical+software+program&w2=Email+software+program&w3=Backup+software+program&w4=Cad+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=L7MT3NCQqcGV882z44fHCw>
> Backup software program
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Medical+software+program&w2=Email+software+program&w3=Backup+software+program&w4=Cad+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=vR1rWTaVtRO_y7ESXba22g>
>
> Cad software program
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Medical+software+program&w2=Email+software+program&w3=Backup+software+program&w4=Cad+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=SYA0W-a_6_5BE3F_Nnh0MQ>
> Wedding program software
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Medical+software+program&w2=Email+software+program&w3=Backup+software+program&w4=Cad+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=mUjPZLcHCILZCOjwfG9Giw>
> Anti virus software program
> <http://groups.yahoo.com/gads?t=ms&k=Anti+virus+software+program&w1=Medical+software+program&w2=Email+software+program&w3=Backup+software+program&w4=Cad+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=H_Yz9KZZsBDQL2KMiDx99w>
>
>
>
> ------------------------------------------------------------------------
> YAHOO! GROUPS LINKS
>
> * Visit your group "EnergyPlus_Support
> <http://groups.yahoo.com/group/EnergyPlus_Support>" on the web.
>
> * To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service <http://docs.yahoo.com/info/terms/>.
>
>
> ------------------------------------------------------------------------
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/