[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Outside air problem
EnergyPlus sums all of the zone exhaust flows on the air loop and adjust the
outside air flow to be no less than this. So the outside air flow into the air
loop will be this value, if the system supply flow is at least this much.
However, EnergyPlus does not force system supply flow to increase to meet an
exhaust fan request. Currently, if zone exhaust flow exceeds supply, the
return flow is set to zero and the excess exhaust flow is ignored. This
presents a problem for your case. When the exhaust fan is running, does the
VAV system operate at constant volume supply to this zone? How is the zone
temperature controlled during these hours?
Mike
On 27 Mar 2006 at 10:38, Petra Vaquero wrote:
> Hi!
> My problem remains....
> I have an extraction fan in the same zone where the VAV system is. From
> 9 to 18 h the extraction flow is very high (0.667 m3/s - 100% outside
> air). The VAV system never needs this flow. How can I assure that the
> outside air will be this value?
>
> If it is not possible do you know another way to simulate this?
>
> Thanks
> Petra
>
> Michael J. Witte wrote:
>
> > This should work. In CONTROLLER:OUTSIDE AIR, specify the desired
> > outside air
> > flow rate for "minimum outside air flow rate". This will be the
> > outside air
> > flow rate when the VAV system is at full flow. If you want this to
> > remain
> > fixed, even when the VAV system flow is reduced, then set MinimumLimit
> > to FIXED
> > MINIMUM. One exception is if the VAV system flow is reduced below the
> > specified "minimum outside air flow rate", the outside air flow will
> > be reduced
> > to provide 100% outside air at whatever the system flow rate is for
> > that time.
> >
> > Mike
> >
> >
> > On 24 Mar 2006 at 12:09, dust_broom wrote:
> >
> > > Hi!
> > >
> > > I am using the EnergyPlus to install a VAV system in a building with
> > > several zones and I need to fix my outside air flow value. I tried to
> > > do
> > > it in the Controller:Outside Air function but it doesn't work. The
> > > outside air value is always the autosized one (In all other components
> > > the airflow values are autosized).
> > > Does any one know how to solve my problem?
> > >
> > > Thanks
> > > Petra
> > >
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> > press the
> > > "search" button.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@xxxxxxxx
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> > press the "search" button.
> >
> >
> >
> >
> > SPONSORED LINKS
> > Backup software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Backup+softwar
> e+program&w2=Cad+software+program&w3=Medical+software+program&w4=Wedding+progr
> am+software&w5=Email+software+program&w6=Anti+virus+software+program&c=6&s=176
> &.sig=T8fEdj-3bpEqOzZAIWj2NQ>
> > Cad software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Backup+software+p
> rogram&w2=Cad+software+program&w3=Medical+software+program&w4=Wedding+program+
> software&w5=Email+software+program&w6=Anti+virus+software+program&c=6&s=176&.s
> ig=UpHLEMEo3UqDXPaxfQGgpQ>
> > Medical software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Backup+softwa
> re+program&w2=Cad+software+program&w3=Medical+software+program&w4=Wedding+prog
> ram+software&w5=Email+software+program&w6=Anti+virus+software+program&c=6&s=17
> 6&.sig=hIggffKyYt6Ha45Qp4vHNw>
> >
> > Wedding program software
> >
> <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Backup+softwa
> re+program&w2=Cad+software+program&w3=Medical+software+program&w4=Wedding+prog
> ram+software&w5=Email+software+program&w6=Anti+virus+software+program&c=6&s=17
> 6&.sig=-fHbdfOtSsOofChL2KuS9g>
> > Email software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Backup+software
> +program&w2=Cad+software+program&w3=Medical+software+program&w4=Wedding+progra
> m+software&w5=Email+software+program&w6=Anti+virus+software+program&c=6&s=176&
> .sig=YkDt0mNOZPgKrXjtZWwLlA>
> > Anti virus software program
> >
> <http://groups.yahoo.com/gads?t=ms&k=Anti+virus+software+program&w1=Backup+sof
> tware+program&w2=Cad+software+program&w3=Medical+software+program&w4=Wedding+p
> rogram+software&w5=Email+software+program&w6=Anti+virus+software+program&c=6&s
> =176&.sig=PaTSxrlhV1VUf3islz2XNA>
> >
> >
> >
> > ------------------------------------------------------------------------
> > YAHOO! GROUPS LINKS
> >
> > * Visit your group "EnergyPlus_Support
> > <http://groups.yahoo.com/group/EnergyPlus_Support>" on the web.
> >
> > * To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
> >
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service <http://docs.yahoo.com/info/terms/>.
> >
> >
> > ------------------------------------------------------------------------
> >
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/