Rory,
There are several ways to do night ventilation. With the Ventilation
object, I think you
are stuck with the fluctuations. But you should look at the example file
5ZoneNightVent3.idf
for an example of a more sophisticated way of doing night ventilation using
SYSTEM AVAILABILITY MANAGER:NIGHT VENTILATION and FAN:NIGHT VENT
PERFORMANCE.
This strategy is fully documented in the IO ref manual and the
Engineering document. You could
also try, if you are willing to use unaltered fan and system
performance, just using night setback
zone setpoints and using the minimum outside air schedule to force 100%
outside air at night.
This schedule is referenced in the OA Controller.
Fred Buhl
Rory Walsh wrote:
>Hello All
>
>I have some instability in one of my models.
>
>It is being caused by a ventilation object which is included to
>provide a simple night ventilation strategy, in an office building.
>Using the ventilation object, ventilation is provided @ 3ACH if the
>internal temperature is above 20C.
>
>I have noticed in the results that the internal temperatures are
>oscillating around 20C during the early morning hours before
>occupation, during summer months.
>This is happening because night ventilation is alternating between on
>and off between each time step, (using 10 minute time steps).
>The oscillations in temperature are not very big, max amplitude is
>about 1C, but this is enough to impact significantly on the comfort
>predictions from my model.
>
>I have also implemented night ventilation using a unit ventilator in
>another model but I am encountering the same problem.
>
>Is it possible to modulate ventilation based on an internal
>temperature only, instead of modulating it based on a temperature
>difference between inside and outside?
>
>I was hoping somebody might have a simple work around.
>
>Best Wishes
>
>Rory
>
>
>
>
>
>
>
>Rory Walsh
>UCD Energy Research Group
>School of Architecture, Landscape & Civil Engineering
>University College Dublin
>Richview, Belfield, Dublin 4, Ireland.
>http://erg.ucd.ie
>
>
>Tel: +353-1-716 2682
>Fax: +353-1-283 8908
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/