Re: [EnergyPlus_Support] Re: Unit Ventilator
This error messages means that "NODE 14066 IN" is listed as a Zone Inlet node,
but there is no component that has the same node name as an outlet node. Thus,
this inlet node will have no flow. Perhaps this is an extra zone inlet node
that is not intended to be connected to anything?
Mike
On 27 Mar 2006 at 14:54, Rory Walsh wrote:
>
>
> Hello all
>
> I am getting the following warning when I use a unit ventilator in
> one of my simulations.
>
> ** Severe ** Error in Node="NODE 14066 IN", ZoneInlet node did not
> find an outlet node.
> ** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION,
> Name=14066
>
> The unit ventilator seems to be working properly but I would prefer
> to know exactly why this error is appearing.
>
> Hope somebody can help
>
> Thanks in advance.
>
> Rory
>
>
>
>
>
>
> Rory Walsh
> UCD Energy Research Group
> School of Architecture, Landscape & Civil Engineering
> University College Dublin
> Richview, Belfield, Dublin 4, Ireland.
> http://erg.ucd.ie
>
>
> Tel: +353-1-716 2682
> Fax: +353-1-283 8908
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/