[EnergyPlus_Support] Re: A zone setpoint control anomaly with ‘dual setpoint with deadband'
Hi Fred,
After checking the EIO file, thats what it seems to be, there is no
cooling load in Zone B during the summer design day.
Thanks for that.
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@...>
wrote:
>
> Elmer,
>
> One thing that happens when you have the 2 setpoints is that the
program
> may be calculating a cooling load for 1 or more zones in the
summer. If that
> happens, the system will be looking at 23 degrees, not 20. So it
will
> reheat the air
> to 23C (assuming the air coming in is less than 23), rather than
heating
> to 20. In
> the soon-to-be-released version we have attempted to eliminate
this
> behavior - the
> system will only reheat to the lowest setpoint temperature.
>
> Fred Buhl
>
> Elmer Morrissey wrote:
>
> >Hello all,
> >
> >I would like to know the significance of using `dual setpoint with
> >deadband' with a system that does not have a cooling coil. I was
using
> >this control for my zone thermostat but I noticed an anomaly. My
> >system contains an economizer, supply fan, heating coil and
terminal
> >reheat coils.
> >
> >The heating setpoints are set to 20C. The cooling setpoints are
set to
> >23C.
> >
> >I was under the impression that since the system is only heating
the
> >air (and letting hot air through without any additional tempering
if
> >OA temps are too high), then zone temps would be kept at 20C year
round.
> >
> >The system itself is supplying air to three zones. If I run the
> >simulation, all system functions seem to work fine except for an
> >anomaly in the zone temps. During the winter: the zones are kept
at
> >20C. However, during the summer: Zone A and Zone C are kept at 23C
> >while Zone B is kept at 20C. All three zones have been set up the
same.
> >
> >Can anyone help me in trying to figure out why this is happening?
> >
> >Kind regards
> >
> >-Elmer
> >
> >
> >
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the "search" button.
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/