Hi Richard,

I checked that out and I am still getting all the same problems. 
I've subbitted the file called in CC.idf  to the problems submittals 
section. I really appreciate the help.

Kind regards

-Elmer

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
<RRaustad@...> wrote:
>
> Even a constant volume plant should shut down when there is no 
call for 
> cooling. Are you sure there is no flow through any of the cooling 
coils? 
> Is the demand side bypass pipe flow rate EQUAL to the supply side 
flow 
> rate at these times? If there is no flow through any cooling coils 
and 
> the demand bypass is equal to the supply flow rate (these are the 
first 
> checks to be verified), then submit your file to the EnergyPlus 
Support 
> Group for further study.
> 
> Elmer Morrissey wrote:
> 
> > Hi,
> >
> > That makes sense. I had a constant volumetric flow rate, so even
> > though the unit was not required to do any work (the cooling 
coil's
> > operations was never requested), the system WAS requesting 7C at 
the
> > outlet of the loop year round.
> >
> > I scheduled this loop to off during the winter months. This took
> > care of the errors however I noticed that there is still a flow
> > through the system!!!? Any idea why this would remain operating?
> >
> > However, I still have two issues with the system.
> >
> > (1) In the summer, the system is not pulling the cooling coil air
> > outlet node temp to 12C. It gets close, but never all the way 
during
> > peak times. The system if fully autosized..
> >
> > (2) The .err file says that "Loads Initialization did not 
Converge
> > (CheckWarmupConvergence)"
> >
> > I've tried increasing the warmup days to 40 but this doesn't 
seem to
> > have an effect.
> >
> > Kind regards
> >
> > -Elmer
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > The message is warning you that an "air cooled" chiller is
> > operating
> > > when outdoor temperatures are below 0C. This type of operation
> > could
> > > freeze the chiller barrel and damage the unit. Good thing it is
> > only a
> > > simulation. What type of loads are in your building that 
require
> > cooling
> > > when it is 0C outside? How about scheduling you chiller off in 
the
> > > winter and using an economizer.
> > >
> > >
> > > Elmer Morrissey wrote:
> > >
> > > > Hello all,
> > > >
> > > > I'm am getting the following error from an electric chiller 
(air
> > > > cooled) which supplies the cool water at 7C for the cooling 
coil
> > in
> > > > the AHU...
> > > >
> > > > ElectricChillerModel:Air Cooled Condenser Inlet Temperature
> > below 0C
> > > > continues
> > > >
> > > > Can anyone point me where I would remove this error?
> > > >
> > > > My chiller definition looks like this
> > > >
> > > > CHILLER:ELECTRIC,
> > > >     Z1:Plant1,               !- Chiller Name
> > > >     AIR COOLED,              !- Condenser Type
> > > >     autosize,                !- Nominal Capacity {W}
> > > >     3.2,                     !- COP
> > > >     Z1:Plant1In,             !- Plant_Side_Inlet_Node
> > > >     Z1:Plant1Out,            !- Plant_Side_Outlet_Node
> > > >     ZC1:Plant1In,            !- Condenser_Side_Inlet_Node
> > > >     ZC1:Plant1Out,           !- Condenser_Side_Outlet_Node
> > > >     0,                       !- Minimum Part Load Ratio
> > > >     1,                       !- Maximum Part Load Ratio
> > > >     0.65,                    !- Opt Part Load Ratio
> > > >     35,                      !- Temp Design Condenser Inlet 
{C}
> > > >     2.778,                   !- Temp Rise Coefficient
> > > >     6.67,                    !- Temp Design Evaporator 
Outlet {C}
> > > >     autosize,                !- Design Evaporator Volumetric
> > Water
> > > > Flow Rate {m3/s}
> > > >     autosize,                !- Design Condenser Volumetric 
Water
> > > > Flow Rate {m3/s}
> > > >     0.9949,                  !- Coefficient1 of the capacity
> > ratio
> > > > curve
> > > >     -0.045954,               !- Coefficient2 of the capacity
> > ratio
> > > > curve
> > > >     -0.0013543,              !- Coefficient3 of the capacity
> > ratio
> > > > curve
> > > >     2.333,                   !- Coefficient1 of the power 
ratio
> > curve
> > > >     -1.975,                  !- Coefficient2 of the power 
ratio
> > curve
> > > >     0.6121,                  !- Coefficient3 of the power 
ratio
> > curve
> > > >     0.03303,                 !- Coefficient1 of the full load
> > ratio
> > > > curve
> > > >     0.6852,                  !- Coefficient2 of the full load
> > ratio
> > > > curve
> > > >     0.2818,                  !- Coefficient3 of the full load
> > ratio
> > > > curve
> > > >     5,                       !- Temp Lower Limit Evaporator
> > Outlet
> > > > {C}
> > > >     ConstantFlow;            !- Chiller Flow Mode
> > > >
> > > > I've attempted reducing the design inlet temperature into the
> > > > condenser but it doesn't appear to be making a difference. 
Also
> > the
> > > > cooling coil is not reducing the temperature of the outlet 
air
> > > > stream to the desired temp of 12C. It gets close (13C) but 
never
> > > > quite down there at peak times.
> > > >
> > > > I appreciate the help, kind regards
> > > >
> > > > -Elmer
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > >
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >
> > > > Attachments are not allowed -- please post any files to the
> > > > appropriate folder in the Files area of the Support Web Site.
> > > >
> > > > EnergyPlus Documentation is searchable.  Open 
EPlusMainMenu.idf
> > and
> > > > press the "search" button.
> > > >
> > > >
> > > >
> > > > -------------------------------------------------------------
----
> > -------
> > > > YAHOO! GROUPS LINKS
> > > >
> > > >     *  Visit your group "EnergyPlus_Support
> > > >       <http://groups.yahoo.com/group/EnergyPlus_Support>" on 
the
> > web.
> > > >       
> > > >     *  To unsubscribe from this group, send an email to:
> > > >        EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > >       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
> > subject=Unsubscribe>
> > > >       
> > > >     *  Your use of Yahoo! Groups is subject to the Yahoo! 
Terms
> > of
> > > >       Service <http://docs.yahoo.com/info/terms/>.
> > > >
> > > >
> > > > -------------------------------------------------------------
----
> > -------
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL  32922-5703
> > > Phone:   (321) 638-1454
> > > Fax:     (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> > >
> > >
> > > [Non-text portions of this message have been removed]
> > >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
> > appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and 
> > press the "search" button.
> >
> >
> >
> > -----------------------------------------------------------------
-------
> > YAHOO! GROUPS LINKS
> >
> >     *  Visit your group "EnergyPlus_Support
> >       <http://groups.yahoo.com/group/EnergyPlus_Support>" on the 
web.
> >        
> >     *  To unsubscribe from this group, send an email to:
> >        EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
subject=Unsubscribe>
> >        
> >     *  Your use of Yahoo! Groups is subject to the Yahoo! Terms 
of
> >       Service <http://docs.yahoo.com/info/terms/>.
> >
> >
> > -----------------------------------------------------------------
-------
> >
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
> 
> 
> 
> [Non-text portions of this message have been removed]
>






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 