[EnergyPlus_Support] Re: Condenser Loop Flow Rate
Thanks, Mike.
Setting the tower to PASSIVE seems to give the desired result.
Regards,
Jeff
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> My apologies for the delayed response. I believe the problem lies
with having
> a single cooling tower on the condenser loop. Once the tower is
active, it is
> request it's full flow rate.
>
> Try making the tower a PASSIVE component on its branch. I am not
100% sure if
> this will change anything, or it may not work at all. (Sorry, I
can't take
> time today to try this out.)
>
> If that does not work, then you will need to model multiple cooling
towers in
> parallel. With load controls corresponding to the chiller load
controls, then
> the towers should come on in sequence as the chillers do, and the
condenser
> loop flow rate should follow.
>
> If these don't work, please upload your input file.
>
> Mike
>
>
> On 1 Apr 2006 at 4:31, enerdata wrote:
>
> > I have three variable flow chillers and a bypass branch in
parallel
> > between the condenser demand side splitter and mixer, staged with
> > cooling load range based operation. On the supply side, I have a
> > single variable speed intermittent condenser water pump and
single 2
> > speed cooling tower on the supply side with a bypass in parallel.
> >
> > The problem is that the cooling tower and pump operate at 100%
design
> > flow (therefore high energy usage) as though all three chillers
were
> > operating, even when only one chiller operates.
> >
> > I have tried removing the bypass branch on the demand side but
his
> > generates an error. What is the correct arrangement of bypass
branches
> > to simulate the cooling tower and condenser pump flow varying as
the
> > chillers are switched on and off (to model an arrangement where
each
> > chiller has it's own condenser water pump)?
> >
> > Many thanks for your assistance.
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.