Re: [EnergyPlus_Support] about doublefacade



 If the double-facade space is open from bottom to top, then it could be 
modeled as a single thermal zone that is 8 stories high.  The outside surface 
would be one surface 8 stories high.  The inside wall would be 8 surfaces 
stacked on top of each other (assuming that is interacts with 8 different 
interior zones).  

If the double-facade space must be divided into multiple thermal zones, then 
you would use either MIXING or CROSS MIXING for simple specified airflows 
between the zones.  Or a full airflow network could also be described using the 
COMIS model instead of the simple mixing and cross mixing.

What is the function of the steel grating?  If it is simply to shade some of 
the solar gains, then it could be modeled as an interior or exterior shade or 
blind.

Mike


On 4 Apr 2006 at 0:37,  wrote:

> hi
>   i ask you something.
>    
>   i make the double facade. I am studying by example files. 
>    
>   And there are doublefacade.idf. 
>    
>   It is one story building
>    
>   But what i'm trying to do is multystory about 8 stories.
>    
>   how the air pass through floor and celing in the double facade zone?
>    
>   How can i control this? do i have to use only celing and floor? 
>    
>   and another question.
>    
>   can i use material called "steel grating" 
>    
>   Steal grating is using in double facade but i don't know how to use this? 
>    
>   if you have any advice. please help me.
>    
>   thanks advance. 
>    
>    
> 
> 		
> ---------------------------------
> 
> ! 
>   , 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/