[EnergyPlus_Support] Zero flow?



I am currently working with a simple .idf file but am experiencing zero flow 
in the plant loop. This is a test file as I am looking at what we need to do 
to implement radiators. I have been looking at it for some time now and can 
not see why I get the zero flow - perhaps I've been looking at it too long.

Would appreciate it if sombody could have a quick look over the file below 
to see if there is anything simple I have missed.

Many thanks.

Brian
Hevacomp

File reads as follows:
-------------------

Version,1.2.3;
Timestep in hour, 4 ;
Building,Hevacomp, 360 ,City,0.04,0.004,FullExterior,25;
Solution algorithm,CTF;
DaylightSavingPeriod,3 / 26,10 / 28;
AirFlow Model,Simple;
Inside convection algorithm,Detailed;
Outside convection algorithm,Detailed;
Run control,No,No,No,No,Yes;
SurfaceGeometry,LowerRightCorner,CounterClockWise,Relative;
RunPeriod, 4 , 28 , 4 , 28 ,Monday,No,No,No,Yes,Yes;

Location,LONDON, 51.5 ,-0.17 ,0, 36 ;
Material:Regular,MAT1,MediumRough, 0.1 , 0.84 , 1700 , 800 , 0.9 , 0.6 , 0.6 
;
Material:Regular,MAT2,MediumRough, 0.025 , 0.02 , 30 , 1000 , 0.9 , 0.6 , 
0.6 ;
Material:Regular,MAT3,MediumRough, 0.1 , 0.08 , 400 , 1100 , 0.9 , 0.6 , 0.6 
;
Material:Regular,MAT4,MediumRough, 0.015 , 0.16 , 950 , 840 , 0.9 , 0.6 , 
0.6 ;
Material:Regular,MAT5,MediumRough, 0.08 , 0.13 , 1600 , 1000 , 0.05 , 0.01 , 
0.01 ;
Material:Regular,MAT6,MediumRough, 0.016 , 0.56 , 1300 , 1000 , 0.05 , 0.01 
, 0.01 ;
Material:Regular,MAT7,MediumRough, 0.15 , 1.4 , 2100 , 840 , 0.9 , 0.6 , 0.6 
;
Material:Regular,MAT8,MediumRough, 0.05 , 0.41 , 1200 , 840 , 0.9 , 0.6 , 
0.6 ;
Material:Regular,MATFURN1,MediumRough, 0.01 , 0.1 , 600 , 1000 , 0.9 , 0.6 , 
0.6 ;
Material:Regular,MATFURN2,MediumRough, 0.025 , 0.1 , 600 , 1000 , 0.9 , 0.6 
, 0.6 ;
Material:Regular,MATFURN3,MediumRough, 0.2 , 0.1 , 600 , 1000 , 0.9 , 0.6 , 
0.6 ;
Material:Regular,DUMMYmat,MediumRough, 1 , 0.03 , 30 , 1000 , 0.01 , 0.01 , 
0.01 ;
Material:Air,AIR1, 0.1308573 ;

Construction,WALLS-1,MAT1,AIR1,MAT2,MAT3,MAT4;
Construction,ROOFS-16,MAT5,MAT6;
Construction,FLOORS-1,MAT6,MAT7,MAT8;
Construction,FURN1,MATFURN1;
Construction,FURN2,MATFURN2;
Construction,FURN3,MATFURN3;
Construction,DUMMY,DUMMYmat;

!------------>
Material:Regular,MATRAD1,MediumRough, 0.2 , 0.1 , 600 , 1000 , 0.9 , 0.6 , 
0.6 ;
  CONSTRUCTION WITH INTERNAL SOURCE,
    RAD1, !- Name
    2,  !- Source present after layer N1
    2,  !- Temperature calculation requested after layer N2
    1,  !- Dimensions for the CTF calculation
    0.1, !- Tube Spacing {m}
    MATRAD1, !- Outside Layer
    MATRAD1, !- Middle Layer
    MATRAD1; !- Inside Layer
!------------>

Material:Windowglass,GLASS1,SpectralAverage,, 0.006 , 0.78 , 0.07 , 0.07 , 
0.78 , 0.07 , 0.07 , 0 , 0.845 , 0.845 , 1 ;

Construction,WINDOW-1-NOSHADE,GLASS1;

GroundTemperatures, 18 , 18 , 18 , 18 , 18 , 18 , 18 , 18 , 18 , 18 , 18 , 
18 ;

GroundReflectances, 0.2 , 0.2 , 0.2 , 0.2 , 0.2 , 0.2 , 0.2 , 0.2 , 0.2 , 
0.2 , 0.2 , 0.2 ;

Zone,R1,0, 0 , 0 , 0 ,, 1 , 3 , 118.8 ;
Infiltration,R1Infil1,R1,SCHED INFILbasic, 1.64999993642171E-02 ,1,0,0,0;
Lights,R1Lights1,R1,SCHED GAIN1, 792 ,0, 0.12 , 0.18 ,0,GeneralLights;

Surface:HeatTransfer,R1 
Surf1-1,WALL,WALLS-1,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0.5 , 4 
,
  0 , 10 , 0 ,
  0 , 10 , 3 ,
  2 , 10 , 3 ,
  2 , 10 , 0 ;
Surface:HeatTransfer,R1 
Surf2-1,WALL,WALLS-1,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0.5 , 4 
,
  2 , 10 , 0 ,
  2 , 10 , 3 ,
  8 , 10 , 3 ,
  8 , 10 , 0 ;
Surface:HeatTransfer:Sub,R1 Surf3-1-NOSHADE,WINDOW,WINDOW-1-NOSHADE,R1 
Surf2-1,, 0.5 ,,R1 Surf3-1Frame, 1 , 4 ,
  2 , 10 , 1.2 ,
  2 , 10 , 2.8 ,
  8 , 10 , 2.8 ,
  8 , 10 , 1.2 ;
WindowFrameAndDivider,R1 Surf3-1Frame, 0.08336397 , 0 , 0 , 5 ,1.0, 1 , 1 , 
0.9 ,DividedLite,0,0,0,0,0,0,1,1,1,0.9, 0.8 , 0 , 0.8 , 0 , 0.8 ;
Surface:HeatTransfer,R1 
Surf4-1,WALL,WALLS-1,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0.5 , 4 
,
  8 , 10 , 0 ,
  8 , 10 , 3 ,
 10 , 10 , 3 ,
 10 , 10 , 0 ;
Surface:HeatTransfer,R1 
Surf5-1,WALL,WALLS-1,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0.5 , 4 
,
 10 , 10 , 0 ,
 10 , 10 , 3 ,
 10 ,  0 , 3 ,
 10 ,  0 , 0 ;
Surface:HeatTransfer,R1 
Surf6-1,WALL,WALLS-1,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0.5 , 4 
,
 10 ,  0 , 0 ,
 10 ,  0 , 3 ,
  0 ,  0 , 3 ,
  0 ,  0 , 0 ;
Surface:HeatTransfer,R1 
Surf7-1,WALL,WALLS-1,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0.5 , 4 
,
  0 ,  0 , 0 ,
  0 ,  0 , 3 ,
  0 , 10 , 3 ,
  0 , 10 , 0 ;
Surface:HeatTransfer,R1 
Surf8-1,ROOF,ROOFS-16,R1,ExteriorEnvironment,,SunExposed,WindExposed, 0 , 4 
,
  0 , 10 , 3 ,
  0 ,  0 , 3 ,
 10 ,  0 , 3 ,
 10 , 10 , 3 ;
Surface:HeatTransfer,R1 Surf9-1,FLOOR,FLOORS-1,R1,OtherZoneSurface,R1 
Surf9-1,NoSun,NoWind,0, 4 ,
 10 , 10 , 0 ,
 10 ,  0 , 0 ,
  0 ,  0 , 0 ,
  0 , 10 , 0 ;
Surface:HeatTransfer:InternalMass,R1-FURN,FURN2,R1, 39.6 ;

!------------>
Surface:HeatTransfer,SURF-R1-RADIATOR,
 WALL,RAD1,
 R1,
 ExteriorEnvironment,,NoSun,NoWind,0.5,4,
  8,9.95,0.1,  8,9.95,1.1,  2,9.95,1.1,  2,9.95,0.1;
!alternative radiator size extending outside building (half-height, 
double-length)
! 11,9.95,0.1, 11,9.95,0.6, -1,9.95,0.6, -1,9.95,0.1;
!------------>

BRANCH,
 R1RADBRANCH,       !- Branch Name
 0,                         !- Maximum Branch Flow Rate {m3/s}
 LOW TEMP RADIANT SYSTEM:CONSTANT FLOW,  !- Comp1 Type
 R1RAD,      !- Comp1 Name
 RADWATERINLETNODE,     !- Comp1 Inlet Node Name
 RADWATEROUTLETNODE,     !- Comp1 Outlet Node Name
 ACTIVE;                    !- Comp1 Branch Control Type

CONTROLLED ZONE EQUIP CONFIGURATION,
 R1,     !- Zone Name
 R1EQUIPMENT,             !- List Name: Zone Equipment
 ,                          !- Node List or Node Name: Zone Air Inlet 
Node(s)
 ,                          !- Node List or Node Name: Zone Air Exhaust 
Node(s)
 R1ROOMAIRNODEIN,          !- Zone Air Node Name
 R1ROOMAIRNODEOUT;         !- Zone Return Air Node Name

ZONE EQUIPMENT LIST,
 R1EQUIPMENT,             !- Name
 LOW TEMP RADIANT SYSTEM:CONSTANT FLOW,  !- KEY--Zone Equipment Type 1
 R1RAD,       !- Type Name 1
 1,     !- Cooling Priority
 1;     !- Heating Priority

LOW TEMP RADIANT SYSTEM:CONSTANT FLOW,
 R1RAD,
 RADSCHEDULE,
 R1,
 SURF-R1-RADIATOR,
 0.012,
 400,
 OPERATIVE,
 0.0004,
 ,
 75000,
 50,
 0.70,
 0,
 RADWATERINLETNODE,     !- heating water inlet node
 RADWATEROUTLETNODE,     !- heating water outlet node
 RADHEATHIGHWATERTEMP,      !- heating high water temperature schedule
 RADHEATLOWWATERTEMP,       !- heating low water temperature schedule
 RADHEATHIGHCONTROLTEMP,    !- heating high control temperature schedule
 RADHEATLOWCONTROLTEMP;    !- heating low control temperature schedule

Schedule:Compact,RADSCHEDULE,Any,Through:12/31,For:AllDays,Until:24:00,1;
Schedule:Compact,RADHEATHIGHWATERTEMP,Any,Through:12/31,For:AllDays,Until:24:00,50;
Schedule:Compact,RADHEATLOWWATERTEMP,Any,Through:12/31,For:AllDays,Until:24:00,30;
Schedule:Compact,RADHEATHIGHCONTROLTEMP,Any,Through:12/31,For:AllDays,Until:24:00,21;
Schedule:Compact,RADHEATLOWCONTROLTEMP,Any,Through:12/31,For:AllDays,Until:24:00,15;

!------------>
!define the plant heating for use with the radiator

PIPE,X1:BypassDemandPipe,
 X1:BypassDemandIn,X1:BypassDemandOut;

Branch,X1:BypassDemand,,
 PIPE,X1:BypassDemandPipe,
 X1:BypassDemandIn,X1:BypassDemandOut,BYPASS;

PIPE,X1:DemandPipeIn,
 X1DemandIn,X1DemandInA;

PIPE,X1:DemandPipeOut,
 X1DemandOutA,X1DemandOut;

BRANCH,X1:DemandIn,,
 Pipe,X1:DemandPipeIn,
 X1DemandIn,X1DemandInA,Passive;

BRANCH,X1:DemandOut,,
 Pipe,X1:DemandPipeOut,
 X1DemandOutA,X1DemandOut,Passive;

BRANCH LIST,X1:DemandBlist,
 X1:DemandIn,R1RADBRANCH,X1:BypassDemand,X1:DemandOut;

SPLITTER,X1:DemandSplit,
 X1:Demandin,
 R1RADBRANCH,
 X1:BypassDemand;

MIXER,X1:DemandMix,
 X1:DemandOut,
 R1RADBRANCH,
 X1:BypassDemand;

CONNECTOR LIST,
 X1:DemandClist,
 SPLITTER,X1:DemandSplit,
 MIXER,X1:DemandMix;

PLANT LOOP,X1:Loop, Water,X1:LoopOp, X1out,90,1,autosize,0.0001,autosize,
 X1in,X1out,X1:Blist,X1:Clist,
 X1DemandIn,X1DemandOut,X1:DemandBlist,X1:DemandClist,Sequential;

PLANT SIZING,X1:Loop,Heating, 80 , 10 ;

BOILER:SIMPLE,X1:Plant1,NaturalGas,autosize, 0.8 , 80 , autosize , 0.1 , 1 , 
1 , 1 , 0 , 0 ,X1:Plant1In, X1:Plant1Out, 90 ,ConstantFlow, 0 ;

PUMP:CONSTANT SPEED,X1:Pump,X1in,X1inA, autosize , 100000 ,autosize, 0.9 , 0 
,CONTINUOUS;

PLANT EQUIPMENT LIST,X1:Pequip,BOILER:SIMPLE,X1:Plant1;
PLANT OPERATION SCHEMES,X1:LoopOp,HEATING LOAD RANGE BASED 
OPERATION,X1:Control,Psched:1;
HEATING LOAD RANGE BASED OPERATION,X1:Control,0,10000000,X1:Pequip;
SET POINT MANAGER:SCHEDULED,X1:Smanage,TEMP,X1:Tsched,X1:Nlist;
NODE LIST,X1:Nlist,X1out;
Schedule:Compact,X1:Tsched,Any,Through: 12/31,For: AllDays,Until: 24:00, 80 
;
PIPE,X1Bypass,X1:BypassIn,X1:BypassOut;
PIPE,X1:PipeOut,X1OutA,X1out;

BRANCH,X1:in,,PUMP:CONSTANT SPEED,X1:Pump,X1in,X1inA,ACTIVE;

BRANCH,X1:Plant1,,BOILER:SIMPLE,X1:Plant1,X1:Plant1In,X1:Plant1Out,ACTIVE;

BRANCH,X1:Bypass,,PIPE,X1Bypass,X1:BypassIn,X1:BypassOut,BYPASS;

BRANCH,X1:out,,PIPE,X1:PipeOut,X1outA,X1out,PASSIVE;

BRANCH LIST,X1:Blist,X1:in,X1:Plant1,X1:Bypass,X1:out;
CONNECTOR LIST,X1:Clist,SPLITTER,X1:Split,MIXER,X1:Mix;
SPLITTER,X1:Split,X1:In,X1:Plant1,X1:Bypass;
MIXER,X1:Mix,X1:out,X1:Plant1,X1:Bypass;

Schedule:Compact, Psched:1,Any,Through: 12/31,For: AllDays,Until: 
1:00,1,Until: 2:00,1,Until: 3:00,1,Until: 4:00,1,Until: 5:00,1,Until: 
6:00,1,Until: 7:00,1,Until: 8:00,1,Until: 9:00,1,Until: 10:00,1,Until: 
11:00,1,Until: 12:00,1,Until: 13:00,1,Until: 14:00,1,Until: 15:00,1,Until: 
16:00,1,Until: 17:00,1,Until: 18:00,1,Until: 19:00,1,Until: 20:00,1,Until: 
21:00,1,Until: 22:00,1,Until: 23:00,1,Until: 24:00,1;

!------------>

ScheduleType,Any;
Schedule:Compact,SCHED INFILbasic,Any,Through: 12/31,For: AllDays,Until: 
24:00,1.0;
Schedule:Compact,SCHED GAIN1,Any,Through: 12/31,For: AllDays,Until: 
1:00,0,Until: 2:00,0,Until: 3:00,0,Until: 4:00,0,Until: 5:00,0,Until: 
6:00,0,Until: 7:00,0,Until: 8:00,0,Until: 9:00,1,Until: 10:00,1,Until: 
11:00,1,Until: 12:00,1,Until: 13:00,1,Until: 14:00,1,Until: 15:00,1,Until: 
16:00,1,Until: 17:00,1,Until: 18:00,1,Until: 19:00,0,Until: 20:00,0,Until: 
21:00,0,Until: 22:00,0,Until: 23:00,0,Until: 24:00,0;

!report variable,*,Outdoor Dry Bulb,hourly;
!report variable,*,Outdoor Wet Bulb,hourly;
report variable,*,Zone Mean Air Temperature,hourly;
!report variable,*,Zone Mean Radiant Temperature,hourly;
!report variable,*,Surface Inside Temperature,hourly;
!report variable,*,Surface Int Convection Coeff,hourly;
report variable,*,Zone Transmitted Solar,hourly;
!report variable,*,Zone Total Internal Latent Gain,hourly;
!report variable,*,Zone Infiltration Sensible Heat Loss,hourly;
!report variable,*,Zone Infiltration Sensible Heat Gain,hourly;
!report variable,*,Electric Equipment Radiant Heat Gain,hourly;
!report variable,*,Electric Equipment Convective Heat Gain,hourly;
!report variable,*,Lights Total Heat Gain,hourly;
!report variable,*,Zone People Sensible Heat Gain,hourly;
!report variable,*,Zone People Latent Heat Gain,hourly;

report variable,*,System Node Temp,hourly;
report variable,*,System Node MassFlowRate,hourly;

Report,surfaces,detailswithvertices;
Report,construction;
Report,variable dictionary; 




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/