On 7 Apr 2006 at 18:46, Sam Roose wrote:
> I have uploaded a file named 18_manager_changes that when run in Version
> 1.2.3.031 gives me three errors.
>
> 1) Calculated design heating load for zone = OUTPATIENT 2 is zero. Check
> zone sizing and zone thermostat inputs.
>
> The specification for OUTPATIENT 2 is no different to the other zones
> with respect to zone sizing and zone thermostat inputs. Hopefully, this
> isn't due to the use of multiple air loops.
>
1. This means the zone has no need for heating on the heating design day. The
zone sizing calculation only relies on the building envelope, thermostat, and
zone sizing objects. It knows nothing of the HVAC system at this point in the
calculation, including any fresh air the HVAC system may be introducing. So,
this is a loads balance issue for the winter design day. If I'm reading the
drawing and inputs correctly, this zone is a large, part interior, part
exterior zone with a small amount of glass. So this result may be correct, but
you should double check the internal gains.
The zone loads are used only to determine the air volume flow rate for that
zone. The system coils are then sized to deliver the specified supply air
temperatures are that flow rate, so the coil load will include the outside air
loads.
> 2) Maximum iterations exceeded for three different air loops: Zone 7, Zone 8
> and Zone 23, all quite large zones and mostly internal to the building. Why
> is this?
2. Max iteration errors indicate the system could not converge on a solution.
This can be due to inconsistent controls causing battling, or a variety of
other reasons. I see two problems in the controller:simple inputs:
2a. There are HUMIDISTAT and SET POINT MANAGER:SINGLE ZONE MAX HUM objects, so
I presume you want humidity control. All of the cooling coi controllers are
currently set for Control variable = TEMP. For humidity control these must be
set to TEMPandHUMRAT. They are currently controlling just for the dry bulb
setopint. (I've posted a suggestion to warn of this condition.)
2b. The supply duct heating coil controllers (I'm presuming these are reheat
for the humidity control) are using "Zone 4 Cooling Coil Outlet Node" as the
control node, but that is the air inlet to the coil. This most likely why
there are max iteration errors and poor control. To fix this, change the
control node to be the heating coil air outlet node (e.g. Zone 1 Air Loop
Outlet Node). This node also needs a setpoint. In the SET POINT
MANAGER:SINGLE ZONE REHEAT, the "Name of the set point Node or Node List" needs
to be a node list which lists both the cooling coil outlet node and the air
loop outlet node (which is the heating coil outlet).
2c. I am a bit puzzled at this system configuration. The way it is described
now, it appears that the cooling coil and heating coil in the main air loop
branch will do all of the control and the zone-level reheat coil is
unneccessary.
Mike
>
> 3) Temperatures out of comfort range, despite everything being autosized.
> Mostly it is a result of overheating due to this building having high
> internal gains. However, the number of hours temperatures are out of range
> is high in some cases. Can this be reduced?
>
> Thanks in advance,
>
> Sam Roose
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/