[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Errors in some zones and not others
Thanks Mike should have seen the humidity rate issue. I still have the
same errors as before, although I have sent an updated attempt based on the
5ZoneBoilerOutsideAirReset example file (in terms of the nodes used at
least). This is called ³20_Node_Changes²
Referring to reply 2b, my attempts to run a simulation with the separate
single zone reheat node list did not work. I gather the approach is to leave
the existing node list as they are and make a new one for the ³single zone
reheat² control? I am not sure I understand the instructions or the need for
two node Ids in that case.
You make a good point about the heating coil within the air loop and the
reheat coil being excessive. Is there an example file with just a cooling
coil and a heating coil in an air loop? I can¹t seem to find one. Thanks for
your help thus far.
Sam
On 4/13/06 3:14 AM, "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
>
>
> On 7 Apr 2006 at 18:46, Sam Roose wrote:
>
>> > I have uploaded a file named 18_manager_changes that when run in Version
>> > 1.2.3.031 gives me three errors.
>> >
>> > 1) Calculated design heating load for zone = OUTPATIENT 2 is zero. Check
>> > zone sizing and zone thermostat inputs.
>> >
>> > The specification for OUTPATIENT 2 is no different to the other zones
>> > with respect to zone sizing and zone thermostat inputs. Hopefully, this
>> > isn't due to the use of multiple air loops.
>> >
>
>
> 1. This means the zone has no need for heating on the heating design day.
> The
> zone sizing calculation only relies on the building envelope, thermostat, and
> zone sizing objects. It knows nothing of the HVAC system at this point in the
> calculation, including any fresh air the HVAC system may be introducing. So,
> this is a loads balance issue for the winter design day. If I'm reading the
> drawing and inputs correctly, this zone is a large, part interior, part
> exterior zone with a small amount of glass. So this result may be correct,
> but
> you should double check the internal gains.
>
> The zone loads are used only to determine the air volume flow rate for that
> zone. The system coils are then sized to deliver the specified supply air
> temperatures are that flow rate, so the coil load will include the outside air
> loads.
>
>> > 2) Maximum iterations exceeded for three different air loops: Zone 7, Zone
8
>> > and Zone 23, all quite large zones and mostly internal to the building. Why
>> > is this?
>
> 2. Max iteration errors indicate the system could not converge on a solution.
> This can be due to inconsistent controls causing battling, or a variety of
> other reasons. I see two problems in the controller:simple inputs:
>
> 2a. There are HUMIDISTAT and SET POINT MANAGER:SINGLE ZONE MAX HUM objects,
> so
> I presume you want humidity control. All of the cooling coi controllers are
> currently set for Control variable = TEMP. For humidity control these must be
> set to TEMPandHUMRAT. They are currently controlling just for the dry bulb
> setopint. (I've posted a suggestion to warn of this condition.)
>
> 2b. The supply duct heating coil controllers (I'm presuming these are reheat
> for the humidity control) are using "Zone 4 Cooling Coil Outlet Node" as the
> control node, but that is the air inlet to the coil. This most likely why
> there are max iteration errors and poor control. To fix this, change the
> control node to be the heating coil air outlet node (e.g. Zone 1 Air Loop
> Outlet Node). This node also needs a setpoint. In the SET POINT
> MANAGER:SINGLE ZONE REHEAT, the "Name of the set point Node or Node List"
> needs
> to be a node list which lists both the cooling coil outlet node and the air
> loop outlet node (which is the heating coil outlet).
>
> 2c. I am a bit puzzled at this system configuration. The way it is described
> now, it appears that the cooling coil and heating coil in the main air loop
> branch will do all of the control and the zone-level reheat coil is
> unneccessary.
>
> Mike
>
>
>> >
>> > 3) Temperatures out of comfort range, despite everything being autosized.
>> > Mostly it is a result of overheating due to this building having high
>> > internal gains. However, the number of hours temperatures are out of range
>> > is high in some cases. Can this be reduced?
>> >
>> > Thanks in advance,
>> >
>> > Sam Roose
>> >
>> >
>> >
>> >
>> > The primary EnergyPlus web site is found at:
>> > http://www.energyplus.gov
>> >
>> > The group web site is:
>> > http://groups.yahoo.com/group/EnergyPlus_Support/
>> >
>> > Attachments are not allowed -- please post any files to the appropriate
>> folder
>> > in the Files area of the Support Web Site.
>> >
>> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
>> the
>> > "search" button.
>> >
>> > Yahoo! Groups Links
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
>
>
>
> YAHOO! GROUPS LINKS
>
> * Visit your group "EnergyPlus_Support
> <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
> *
> * To unsubscribe from this group, send an email to:
> * EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
> *
> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
> <http://docs.yahoo.com/info/terms/> .
>
>
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/