Hi Mike,
Thanks for getting back to me so quickly.
Re: 2) I am doing a design day.
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> 1. This will be undersized, because the temperature difference in
the
> denominator needs to be a log mean temperature difference which
includes the
> leaving air and water temperatures, which you do not know. (A new
way of
> inputting baseboard heat capacity is in the plan for the future.)
>
> 2. I am not sure I can explain why the peak output is smaller
thatn the
> heating design load. Are the simulation outputs from "Do the
design day
> simulations" or "Do the weather file simulation"?
>
> 3. There is a bug in the user specification of UA for the
baseboard. This has
> been fixed for the 1.3.0 release which will be available soon.
>
> Mike
>
>
> On 25 Apr 2006 at 16:45, Elmer Morrissey wrote:
>
> > Hello all,
> >
> > I have a question pertaining to autosizing BASEBOARD
> > HEATER:Water:Convective objects.
> >
> > In the simulation model, the BASEBOARD HEATER:Water:Convective
> > objects are the only energy tempering devices in the room.
> >
> > Simulation Run 1: Set the UA from UA = q(loss) / (t(water)-t
(air))
> > and autosize water flow rate
> > If I run the simulation and concentrate on one particular zone,
the
> > heating design load is 718.55 W. Assuming the room temp is 20C
and
> > the water temp is 80C, this would leave a UA of 11.98 W/dK.
However,
> > if you use this values in the input configuration for UA: (1)
the
> > zone temperature is not consistently maintained at 20C and (2)
the
> > maximum load from the heater is never greater than 360.81 W.
> >
> > Simulation Run 2: Autosize the UA and water flow rate
> > EnergyPlus calculates the values of UA to be 18.933. The zonal
> > conditions are spot on. The only odd behaviour is that the max
> > output from the heater is never greater than 600 W.
> >
> > Simulation Run 3: Set the UA from the last run and water flow
rate
> > Now the zonal conditions are not maintained even though nothing
was
> > changed except manually configuring the UA syntax to the
autosized
> > value from the previous run.
> >
> > Can anyone explain this?
> >
> > Kind regards
> >
> > -Elmer
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.