RE: [EnergyPlus_Support] Heated surfaces



I am not sure why you expect the surface temperature to approach the mean of the water.   That surface temperature is modeled with a comprehensive heat balance that includes convection and radiation with the other surfaces in the zone.  The surface is heating the room (and its surfaces) and along with that comes energy flowing from the pipes to the surface.  There has to be a temperature drop associated with that energy flow.   Although your pipes are close together, there isn't a continuous layer of them located right at the surface.   Assuming your values are in degrees C, I don't immediately see a problem with those results. 
 
 

-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of tonybaxterhevacomp
Sent: Monday, May 08, 2006 10:45 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Heated surfaces


Hello anyone,

I have set up a LOW TEMP RADIANT SYSTEM:HYDRONIC system, using heated 
surfaces.  Everything works fine, but I have a question relating to 
the surface temperature of the heated surfaces.

I am using a boiler (Flow 80, return 70) to serve the pipe coils in 
the heated surfaces.  The coils are spaced fairly closely  at 200mm.  
The heated surface has a metal plate front material and 100mm backing 
insulation.  The maximum surface temperature I have seen for the 
heated surfaces is around 60, whilst I would have expected it to 
approach the mean water temperature of 75.

Not knowing what surface temperatures are likely makes it difficult 
to predict the required area of heated surface.

Could anybody help on this.

Tony Baxter







The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.





SPONSORED LINKS 
Email  <http://groups.yahoo.com/gads?t=ms&k=Email+software+program&w1=Email+software+program&w2=Medical+software+program&w3=Cad+software+program&w4=Backup+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=VA_mdi2DwKS3iKGjFCecoA> software program 	Medical  <http://groups.yahoo.com/gads?t=ms&k=Medical+software+program&w1=Email+software+program&w2=Medical+software+program&w3=Cad+software+program&w4=Backup+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=ktRONyYbgAJovLlxNFFxwA> software program 	Cad  <http://groups.yahoo.com/gads?t=ms&k=Cad+software+program&w1=Email+software+program&w2=Medical+software+program&w3=Cad+software+program&w4=Backup+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=T17ECfLRwMzbjAw9ad6Ouw> software program 	
Backup  <http://groups.yahoo.com/gads?t=ms&k=Backup+software+program&w1=Email+software+program&w2=Medical+software+program&w3=Cad+software+program&w4=Backup+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=7pfuV_oXp4sqymT60YxAWQ> software program 	Wedding  <http://groups.yahoo.com/gads?t=ms&k=Wedding+program+software&w1=Email+software+program&w2=Medical+software+program&w3=Cad+software+program&w4=Backup+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=WxH2_6BiyGmc_meTpK79lg> program software 	Anti  <http://groups.yahoo.com/gads?t=ms&k=Anti+virus+software+program&w1=Email+software+program&w2=Medical+software+program&w3=Cad+software+program&w4=Backup+software+program&w5=Wedding+program+software&w6=Anti+virus+software+program&c=6&s=176&.sig=NMb_nG_e2tqBVO25ZUlU1w> virus software program 	

  _____  

YAHOO! GROUPS LINKS 


	
*	 Visit your group " EnergyPlus_Support <http://groups.yahoo.com/group/EnergyPlus_Support> " on the web.
  

*	 To unsubscribe from this group, send an email to:
  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
  

*	 Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 


  _____  




[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Get to your groups with one click. Know instantly when new email arrives
http://us.click.yahoo.com/.7bhrC/MGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/