RE: [EnergyPlus_Support] static pressure setpoint
The "Delta Pressure" variable is not the same as the supply duct static
pressure or the static pressure setpoint. According to the documentation,
Delta Pressure is "The pressure rise in Pascals at full flow and standard
(sea level) conditions (20o C and 101325 Pa)."
Is Delta Pressure the static pressure or the total pressure? From an
offline conversation about this subject, my understanding now is that
EnergyPlus doesn't compute duct pressures. If that is true, then what does
EnergyPlus do with Delta Pressure? If it is false, then can duct pressure
be the control variable of a Controller object?
At 08:57 AM 5/12/2006, you wrote:
>the static pressure is set in the fan object. Note that it is a constant.
>
>
>
>-----Original Message-----
>From: EnergyPlus_Support@xxxxxxxxxxxxxxx
>[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Clifford Federspiel
>Sent: Friday, May 12, 2006 9:31 AM
>To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>Subject: [EnergyPlus_Support] static pressure setpoint
>
>
>How do I set the supply duct static pressure setpoint of a VAV system?
>
>
>Clifford Federspiel, PhD, PE
>Principal, Federspiel Controls, LLC
>828 San Pablo Avenue, Suite 115E, Albany, CA 94706-1693
>v: 510-418-3392 | f: 510-526-4309 | cf@xxxxxxxxxxxxxxxxxxxxxx
>www.federspielcontrols.com
>
>
>
>The primary EnergyPlus web site is found at:
><http://www.energyplus.gov>http://www.energyplus.gov
>
>The group web site is:
><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
>the "search" button.
>
>
>
>
> _____
>
>YAHOO! GROUPS LINKS
>
>
>
>* Visit your group " EnergyPlus_Support
><<http://groups.yahoo.com/group/EnergyPlus_Support>http://groups.yahoo.com/group/EnergyPlus_Support>
>" on the web.
>
>
>* To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
>
>* Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
><<http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/> .
>
>
> _____
>
>
>
>
>[Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
><http://www.energyplus.gov>http://www.energyplus.gov
>
>The group web site is:
><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
>the "search" button.
>
>
>
>
>----------
>YAHOO! GROUPS LINKS
>
> * Visit your group
> "<http://groups.yahoo.com/group/EnergyPlus_Support>EnergyPlus_Support" on
> the web.
> *
> * To unsubscribe from this group, send an email to:
> *
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> *
> * Your use of Yahoo! Groups is subject to the
> <http://docs.yahoo.com/info/terms/>Yahoo! Terms of Service.
>
>
>----------
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Everything you need is one click away. Make Yahoo! your home page now.
http://us.click.yahoo.com/AHchtC/4FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/