[EnergyPlus_Support] Re: humidity control



Thanks very much!I will check again.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@...> wrote:
>
> 1.  The zone supply air flow rates are calculated by ZONE SIZING 
based on 
> sensible load requirements, so the SYSTEM SIZING object will not 
alter the air 
> flow rates.  Also, note that the "type of load to size on" field in 
the SYSTEM 
> SIZING object only accepts "sensible" (see Input Output 
Reference).  I see that 
> the IDD file does not mention this, so I will add a note.
> 
> 2. In the file you submitted last week, in CONTROLLER:OUTSIDE AIR, 
ECONOMIZER 
> is active.  If that is active in your current idf, then that would 
explain the 
> increase in outside air flow.
> 
> 3. Check the setpoint controls on the main heating coil.  It should 
attempt to 
> heat the air to the desired setpoint, assuming that the entering 
hot water 
> temperature is adequate.
> 
> Mike
> 
> 
> On 6 Jun 2006 at 9:26, hbn_pch wrote:
> 
> > Mike,i report the system node temp and system node 
volflowrate,find 
> > that system node temp is low enough(perhaps had achieved dew 
point) 
> > but system node volflowrate remain max(sizing in eio).It seems 
that 
> > the air loop capability is sized too small.Then i adjust the 
sizing 
> > parameter to 2 and find it can control temp and hum well.I try 
> > another model for a test,find it should set sizing parameter to 3 
for 
> > control aim.All is autosized in the model.Why is it sized so 
small?
> > Does it just sized the sensible load?But when i change the size 
type 
> > in system sizing to total,the result did not change yet.
> > 
> > question 2 :I set 0.0094m3/s in the zone sizing for outside air 
and 
> > oa method is flow/person.There is 20 people in the zone,min oa 
remain 
> > 1.So for all day,the outside air volflowrate should remain 
> > 0.188m3/s.But for simulation ,i find sometimes the outside air 
> > volflowrate would increase.What caused this change?
> > 
> > question 3 :When i use vav:reheat,i set the vav outlet node temp 
in 
> > winter to 16.I find in winter design day,the vav damper remain 
min 
> > and the vav outlet node temp did not achieve setpoint temp.I 
checked 
> > other simulation day,find that the vav outlet node temp did't not 
> > achieved setpoint at all,sometimes are very small.Then it will be 
> > reheated by reheat coil .How did the main heating coil and reheat 
> > coil distribue the heating task?
> > 
> >   Appreciated your kind help.
> >   PCH
> > 
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "mjwitte" <mjwitte@> 
> > wrote:
> > >
> > > If you report the System Node Setpoint Temp at the air loop 
outlet
> > > node, you will see that the controller is trying to control to 
the
> > > specified RH setpoint, but the cooling coil is unable to supply 
air
> > > that is cold enough to meet this.  I tried making some changes 
to 
> > get
> > > this to autosize to a better result, but have not been 
successful 
> > yet.
> > > 
> > > Mike
> > > 
> > > 
> > > 
> > > 
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "hbn_pch" <hbn_pch@> 
> > wrote:
> > > >
> > > > Dear,
> > > >    I want to control humidity for a single zone.I create the 
> > model like 
> > > > the examplefile '5ZoneWaterCooled_HighRHControl.idf',but the 
Zone 
> > Air 
> > > > Relative Humidit was not controlled to setpoint in my 
model,while 
> > the 
> > > > examplefile can.
> > > >    I really can't find the problems.appreciated your kind 
> > help.I've 
> > > > upload  correlative file named 'RH CONTROL.zip'
> > > >    Thanks very much
> > > >    pch
> > > >
> > >
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and press the
> > "search" button.
> >  
> > Yahoo! Groups Links
> > 
> > 
> > 
> >  
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>







------------------------ Yahoo! Groups Sponsor --------------------~--> 
Everything you need is one click away.  Make Yahoo! your home page now.
http://us.click.yahoo.com/AHchtC/4FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/