The only ones available to you in the outside air system are:
COIL:Gas:Heating
COIL:Electric:Heating
DXSystem:AirLoop
Check the IO Ref for input details. In each case you need to specify the
setpoint node.
Fred Buhl
hbn_pch wrote:
>Thanks for you response.As you said ,which component should i add to
>the upstream of the mixer for reheat/recool?Which component has its
>own built-in controllers?
>
> thanks
> pch
>--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@...>
>wrote:
>
>
>>Sorry - the program can not do what you would like it to do. The
>>Controller:Simple
>>will only function in the main air loop; it does not work in the
>>
>>
>outside
>
>
>>air system. Components
>>in the outside air stream must have their own built-in controllers
>>
>>
>to
>
>
>>control to a setpoint. Chilled
>>and hot water coils do not have built-in control.
>>
>>Fred Buhl
>>
>>hbn_pch wrote:
>>
>>
>>
>>>I want to recool/reheat the outside air(OA) to the specified
>>>
>>>
>setpoint
>
>
>>>temp(usually dewpoint temp for dehumidify in summer).So i add a
>>>
>>>
>cooling
>
>
>>>coil,a heating coil at upstrem of the OA mixer.The OA flow as
>>>
>>>
>follows:
>
>
>>> Outside Air--->Cooling Coil--->Heating Coil--->OA mixers
>>>For OA temp control(inlet node of the oa mixer),i tried to add two
>>>simple controller to control the cooling/heating coil.After
>>>simulation,it seems ok and there is no serveres.But there is a
>>>
>>>
>orphaned
>
>
>>>branch exist.I check the values and find that the outside air
>>>VolFlowRate is 0.Meanwhile,the oa reheat/reheat coil are not sized
>>>
>>>
>in
>
>
>>>*.eio file and the water inlet MassFlowRate is 0.I check the
>>>
>>>
>i/o,and it
>
>
>>>said i can add upstream compent for mixer.I don't know whether my
>>>
>>>
>setup
>
>
>>>for whole system is correct.
>>>
>>> I've upload the file named 'upstream component to mixer'.
>>> Look forward to your kind help.Thanks
>>>
>>> PCH
>>>
>>>
>>>
>>>
>>>
>>>
>>>The primary EnergyPlus web site is found at:
>>>http://www.energyplus.gov
>>>
>>>The group web site is:
>>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>>Attachments are not allowed -- please post any files to the
>>>
>>>
>appropriate folder in the Files area of the Support Web Site.
>
>
>>>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
>>>
>>>
>and press the "search" button.
>
>
>>>Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>
>
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
>
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
You can search right from your browser? It's easy and it's free. See how.
http://us.click.yahoo.com/_7bhrC/NGxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/