Thanks for you response.As you said ,which component should i add to
the upstream of the mixer for reheat/recool?Which component has its
own built-in controllers?
thanks
pch
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@...>
wrote:
>
> Sorry - the program can not do what you would like it to do. The
> Controller:Simple
> will only function in the main air loop; it does not work in the
outside
> air system. Components
> in the outside air stream must have their own built-in controllers
to
> control to a setpoint. Chilled
> and hot water coils do not have built-in control.
>
> Fred Buhl
>
> hbn_pch wrote:
>
> >I want to recool/reheat the outside air(OA) to the specified
setpoint
> >temp(usually dewpoint temp for dehumidify in summer).So i add a
cooling
> >coil,a heating coil at upstrem of the OA mixer.The OA flow as
follows:
> > Outside Air--->Cooling Coil--->Heating Coil--->OA mixers
> >For OA temp control(inlet node of the oa mixer),i tried to add two
> >simple controller to control the cooling/heating coil.After
> >simulation,it seems ok and there is no serveres.But there is a
orphaned
> >branch exist.I check the values and find that the outside air
> >VolFlowRate is 0.Meanwhile,the oa reheat/reheat coil are not sized
in
> >*.eio file and the water inlet MassFlowRate is 0.I check the
i/o,and it
> >said i can add upstream compent for mixer.I don't know whether my
setup
> >for whole system is correct.
> >
> > I've upload the file named 'upstream component to mixer'.
> > Look forward to your kind help.Thanks
> >
> > PCH
> >
> >
> >
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
> >
> >EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the "search" button.
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Home is just a click away. Make Yahoo! your home page now.
http://us.click.yahoo.com/DHchtC/3FxNAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/