[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] COIL:Water:Cooling
Hello anyone,
I have set up a simple constant volume a/c system, with a chilled
water cooling coil, with water at 7/9 degC. There is zone temperature
control but no humidity control. The sizing results give me an all
sensible load of 6.5kW (ie no dehumid). I noticed that I was
using 'autosize' for the 'Design Outlet Air Humidity Ratio' (DOAHR)
item. When I changed this, the coil performance, not unreasonably,
started to change. I cannot however figure out what is happening to
the coil performance.
The figures for the coil, as I varied DOAHR are:
Coil DOAHR 0.002 0.004 0.006 0.008 0.010 0.012
Coil T out 18.45 16.3 17.1 16.01 18.93 21.2
Coil Hum out 0.00945 0.00828 0.00868 0.01001 0.00976 0.01001
In all cases, the coil Design Inlet Air Humidity Ratio was set
to 'autosize'. The on-coil condition is 28.3C/0.01001
For autosized DOAHR, the off-coil condition is 16C/0.01001
Does anyone know what the 'autosize' option does with the coil
performance and what is happening as DOAHR varies
COIL:Water:Cooling,A3:Cool,Psched:1,autosize,autosize,autosize,autosiz
e,autosize,autosize,autosize,A3In:Cool,A3Out:Cool,A3:SinA,A3:SinB,Simp
leAnalysis,CrossFlow;
Best wishes
Tony Baxter
------------------------ Yahoo! Groups Sponsor --------------------~-->
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/2pRQfA/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/