This coil model is documented in the Engineering Reference, beginning near the 
bottom of p. 421 (pdf p. 453).  The design (autosizing) calculations for the 
coil determine several UA values for the coil and a chilled water flow rate 
which will satisfy the design inlet/outlet conditions.  

The component sizing report for the coil will show the values used and/or 
computed for any field in which "autosize" has been entered.  If the leaving 
air conditions are set to "autosize" they will be taken from cooling supply 
temperature and humidity specified in the SYSTEM SIZING object.  The entering 
and leaving chilled water temperatures are taken from the PLANT SIZING object.  
The entering air conditions are taken from the design day mixed air conditions 
at peak cooling load.

In the numbers below, what is "coil T out"?  Is this a sizing report result or 
a simulation result?

Mike
 

On 26 Jun 2006 at 11:56, tonybaxterhevacomp wrote:

> 
> Hello anyone,
> 
> I have set up a simple constant volume a/c system, with a chilled 
> water cooling coil, with water at 7/9 degC. There is zone temperature 
> control but no humidity control.  The sizing results give me an all 
> sensible load of 6.5kW (ie no dehumid).  I noticed that I was 
> using 'autosize' for the 'Design Outlet Air Humidity Ratio' (DOAHR)
> item.  When I changed this, the coil performance, not unreasonably, 
> started to change.  I cannot however figure out what is happening to 
> the coil performance.
> 
> The figures for the coil, as I varied DOAHR are:
> 
> Coil DOAHR     0.002    0.004    0.006   0.008   0.010    0.012
> Coil T out     18.45    16.3     17.1    16.01   18.93    21.2
> Coil Hum out 0.00945  0.00828  0.00868  0.01001 0.00976  0.01001
> 
> In all cases, the coil Design Inlet Air Humidity Ratio was set 
> to 'autosize'. The on-coil condition is 28.3C/0.01001
> For autosized DOAHR, the off-coil condition is 16C/0.01001
> 
> Does anyone know what the 'autosize' option does with the coil 
> performance and what is happening as DOAHR varies 
> 
> COIL:Water:Cooling,A3:Cool,Psched:1,autosize,autosize,autosize,autosiz
> e,autosize,autosize,autosize,A3In:Cool,A3Out:Cool,A3:SinA,A3:SinB,Simp
> leAnalysis,CrossFlow;
> 
> 
> Best wishes
> 
> Tony Baxter
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Check out the new improvements in Yahoo! Groups email.
http://us.click.yahoo.com/6pRQfA/fOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/