Hi Richard,
I tried what you recommended and it seems I do have a capacity
problem. However I have used the following system sizing:
SYSTEM SIZING,
A3:Loop, !- name of an AIR PRIMARY LOOP object
sensible, !- type of load to size on
autosize, !- Design (minimum) outside air
volumetric flow rate {m3/s}
1, !- minimum system air flow ratio
5, !- Preheat design set temperature {C}
5, !- Central cooling design supply air
temperature {C}
16, !- Central heating design supply air
temperature {C}
noncoincident, !- Sizing Option
Yes, !- Cooling 100% Outside Air
Yes, !- Heating 100% Outside Air
0.0025, !- Central cooling design supply
air humidity ratio {kg-H2O/kg-air}
0.008, !- Central heating design supply
air humidity ratio {kg-H2O/kg-air}
Design day, !- cooling design air flow method
, !- cooling design air flow rate {m3/s}
Design day, !- heating design air flow method
; !- heating design air flow rate {m3/s}
I can maintain around 55% RH during peak hours but I can't get down
to 50%. The SYSTEM NODE SETPOINT TEMP after the cooling coil becomes
as low as -55C during these hours. The `System Node Humidity Ratio
Max' displays similar swings in setpoint.
During the winter, I able to maintain 50% RH most of the day but 4
of the hours display values around the 41% range for some unknown
reason. I checked things like infiltration and I can't seem to
account for it.
I am using one central AHU for zone control. It supplies and
extracts air from the room. It contains a mixer, a CC, a HC, a
humidifier and a supply fan. Finally, it contains a terminal reheat
coil.
I appreciate your help.
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> Are you saying you don't have enough capacity to maintain RH, or
that
> the system is not actively controlling to the RH set point? I
assume you
> already have a humidistat in the control zone. What type of system
are
> you using? If you are using a chilled water coil, the simple
> controller's control variable should be set to TEMPandHUMRAT and a
> single zone max hum set point manager is required to place the set
point
> at the cooling coil outlet node. Report out the temperature set
point
> after the cooling coil, when the RH rises above the set point, the
> temperature set point should start to drop. The higher the
humidity
> rises above the set point, the lower the temperature set point
after the
> cooling coil. If this happens, the system is actively controlling
to the
> RH set point and it is a capacity issue. If you are using DX
> System:AirLoop object, the Run on Latent Load field should be set
to YES
> and the dehumidification control type field should be set to
COOLREHEAT.
> A single zone max hum set point manager is also required to place
the
> humidity set point at the cooling coil outlet node. If you are
using a
> Furnace or Unitary System, all that is required is setting the
high
> humidity control field to YES in the furnace or unitary system
object.
>
> Elmer Morrissey wrote:
>
> > Hello all,
> >
> > I am having major difficulty maintaining 50% RH in a single zone
> > supplied by a simple AHU.
> >
> > Fresh air- -> Fan -> CC -> HC -> Hum -> -----------TRH -> Zone->-
----
> > ------exhaust
> >
> > The max humidity ratio is assigned after the cooling coil while
the
> > minimum humidity ratio is set after the humidifier. I am looking
at
> > a typical design day in a British climate and it should not be
> > overtaxing.
> >
> > Unfortunately, the RH is not maintained during the summer months
> > (even though I oversized the system sizing object). The average
RH
> > is around 57%. During the winter, RH values slip around mid-day
for
> > a four hour period that I cannot explain.
> >
> > I've taken a look at the setpoint output from the CSV file for
the
> > max and min humidity ratios and it seems to me like they just are
> > not be applied within the model. I am aware that humidity
control is
> > not the strongest area in E+ but is there any way of creating a
file
> > that would work for an autosized run?
> >
> > Can anyone help or point out some things I may have overlooked?
> >
> > Kind regards
> >
> > -Elmer
> >
> >
>
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Groups gets a make over. See the new email design.
http://us.click.yahoo.com/XISQkA/lOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/