[EnergyPlus_Support] Re: VAV Boxes
Mike,
Do you think this 'oscillation' with each timestep will produce an
average heating energy input to the zone over, say, a one hour period
sufficient to maintain the space at close to the heating setpoint?
Is the effect therefore similar to a thermostat with slow reactions?
I think the version 1.3.0 modelling is probably still more realistic
than earlier versions in terms of reheat assessment but would be
interested in your views.
Jeff
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> After some digging, we have verified that there is a problem with
the behavior
> of the reheat controls in version 1.3.0 under certain conditions.
Without
> getting into too much detail, if the zone thermostat predicts that
the zone
> would be in the deadband (between the heating and cooling setpoint)
with no
> HVAC operation, it sets a "deadband" flag. When the deadband flag
is active,
> the reheat coil will not operate. If the min flow of cold air from
the VAV
> terminal unit cools the zone below the heating setpoint, the reheat
coil will
> not come on until the next time step. The solution is oscillating
between
> these states. I do not know of a workaround to get this to behave
any better
> in 1.3.0.018.
>
> Mike
>
>
> On 15 Jun 2006 at 11:33, Peter G Loutzenhiser wrote:
>
> >
> > >Hello All,
> >
> >
> > I have just started using the 1.3 version of
> > EnergyPlus with a VAV reheat system and a dual
> > heating/cooling setpoint temperature. I have
> > 13.6°C air entering the coil and I have a heating
> > setpoint of 22°C. I have given the reheat coils
> > plenty of capacity and yet I still get zone
> > temperature below the heating setpoint (in the range of 21.7°C).
Why is
> > this?
> >
> > Peter
> >
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/2pRQfA/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/