RE: [EnergyPlus_Support] AirFlowNetwork simulation and Attached Shading



Hello Lixing

Thanks for your response.
This presents major difficulties for all users, as the AirFlowNetwork model
is unusable for real applications which have external window fins or include
external buildings.

As we are EnergyPlus Developers, is there a temporary fix that we could
make, to tide us over until the next release?

Thanks for your help so far.

Tony Baxter



  -----Original Message-----
  From: Lixing Gu [mailto:gu@xxxxxxxxxxxx]
  Sent: 14 July 2006 13:44
  To: EnergyPlus_Support@xxxxxxxxxxxxxxx
  Subject: Re: [EnergyPlus_Support] AirFlowNetwork simulation and Attached
Shading


  Tony:

  You are right. The AirflowNetwork model can not handle inputs with
external
  shading surfaces. The AirflowNetwork model assumes each surface is exposed
  to a zone, but the external shading surfaces have no zone associated. The
  problem will be fixed in the next release.

  I tried to find a workaround way and could not find any so far.

  Thanks.

  Lixing Gu
  Florida Solar Energy Center
  1679 Clearlake Road
  Cocoa, FL 32922
  Phone: (321) 638-1411
  Fax: (321) 638-1439

  ----- Original Message -----
  From: "Tony Baxter" <tony@xxxxxxxxxxxx>
  To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
  Sent: Wednesday, July 12, 2006 9:38 AM
  Subject: RE: [EnergyPlus_Support] AirFlowNetwork simulation and Attached
  Shading

  >
  > Hello Lixing,
  >
  > I have uploaded a file in Files/Problem_Submittals area tagged
  > AIRFLOWNETWORK and Shading
  > This contains Surface:Shading:Detached:Building.
  > Same problem with simple attached shading
  >
  > Thanks
  >
  > Tony Baxter
  >
  >
  > -----Original Message-----
  > From: Lixing Gu [mailto:gu@xxxxxxxxxxxx]
  > Sent: 12 July 2006 13:38
  > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
  > Subject: Re: [EnergyPlus_Support] AirFlowNetwork simulation and Attached
  > Shading
  >
  >
  > Tony:
  >
  > Could you upload the input files with Surface:Shading:Detached:Building
  > and
  > Surface:Shading:Attached? I will take a look and let you know waht
  > happens.
  >
  > Thanks.
  >
  > Lixing Gu
  > ----- Original Message -----
  > From: "tonybaxterhevacomp" <tony@xxxxxxxxxxxx>
  > To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
  > Sent: Wednesday, July 12, 2006 7:40 AM
  > Subject: [EnergyPlus_Support] AirFlowNetwork simulation and Attached
  > Shading
  >
  > >
  > > Hello again,
  > >
  > > I have also noticed that the AIRFLOWNETWORK SIMULATION model also
fails
  > > when you use Surface:Shading:Detached:Building, eg for external
  > > buildings.
  > >
  > > Tony Baxter
  > >
  > >
  > >
  > >
  > >
  > >
  > > The primary EnergyPlus web site is found at:
  > > http://www.energyplus.gov
  > >
  > > The group web site is:
  > > http://groups.yahoo.com/group/EnergyPlus_Support/
  > >
  > > Attachments are not allowed -- please post any files to the
appropriate
  > > folder in the Files area of the Support Web Site.
  > >
  > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
  > press
  > > the "search" button.
  > >
  > > Yahoo! Groups Links
  > >
  > >
  > >
  > >
  > >
  > >
  > >
  >
  >
  >
  >
  >
  >
  > [Non-text portions of this message have been removed]
  >
  >
  >
  > The primary EnergyPlus web site is found at:
  > http://www.energyplus.gov
  >
  > The group web site is:
  > http://groups.yahoo.com/group/EnergyPlus_Support/
  >
  > Attachments are not allowed -- please post any files to the appropriate
  > folder in the Files area of the Support Web Site.
  >
  > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
  > the "search" button.
  >
  > Yahoo! Groups Links
  >
  >
  >
  >
  >
  >
  >
  >



  


[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Groups gets a make over. See the new email design.
http://us.click.yahoo.com/XISQkA/lOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/