1.  Alongside the walls.  These three fields go together:

Field N3: This specifies the width of the gravel "fill" bed beside the basement 
wall.
Field N4: This specifies the depth of the gravel fill above the floor slab.
Field N5: This specifies the depth of the gravel fill below the floor slab.

2.  There is an "A/P ratio" in the EquivSlab object.  This is the area to 
perimeter ratio of the floor slab only.  I do not know if the 3-D grid 
subdivides the interior space, but this would expect this to have little impact 
on the results.

Mike


On 19 Jul 2006 at 20:02, aboyemeplus wrote:

> 
> Please explain the following input fields for me.
> 
> 1) "Gravel fill above the floor slab"
> Is this gravel fill above the basement floor alongside the walls?    
> Or,is it refering to gravel fill above the slab covering a totally 
> underground building?
> 
> 2) "Aspect Ratio"
> Should the AR be based on the entire heat transfer surface of the 
> underground structure or a single wall? Is the 3-D grid generated for 
> the entire basement, including the enclosed space? Or, does the 
> program generate 3-D grids for each wall and floor slab?
> 
> Thank you for the support.
> 
> Merid   
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Great things are happening at Yahoo! Groups.  See the new email design.
http://us.click.yahoo.com/TISQkA/hOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/