[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Moisture transfer



 1.  EMPD only models moisture storage and release, so it will not model this.  
MTF is intended to model moisture transfer, however the current implementation 
is rather limited due to a single set of linear coefficients when in reality 
the mositure properties are very nonlinear as conditions change.  See the 
cautions in the I/O reference and Engineering Reference in the sections 
regarding moisture material properties.  I do not think that MTF can deal with 
soil as the outside environment.  So, you probably need to find another tool to 
model this moisture transport.

2.  No.  Othersidecoeff has no provision for establishing moisture conditions.

3.  EnergyPlusV1-3-0\DataSets\MoistureMaterials.idf

Mike


On 20 Jul 2006 at 14:53, aboyemeplus wrote:

> I would like to simulate transfer of moisture from the outside 
> surfaces of a basement into the conditioned space. 
> 
> 1.) should the MTF method be used for this application and not the 
> EMPD algorithm?
> 
> 2.)Can I use "Othersidecoeff" boundary conditions when the MTF 
> solution method is selected? 
> 
> 3.) Is there a sample file containing moisture properties data for 
> typical contruction materials?
> 
> Thank you for your support.
> 
> Merid
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Great things are happening at Yahoo! Groups.  See the new email design.
http://us.click.yahoo.com/TISQkA/hOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/