EnergyPlus by default uses a uniform temperature for all of the air in a
thermal zone (well-stirred assumption). Beyond that, there are some options
for limited thermal stratification for displacement ventilation and underfloor
air distribution (UFAD) modeling. There are also models for natural
ventilation, but these assume a well-stirred air mass within a single thermal
zone. To combine open-air wind effects with thermal stratification seems that
it would require a CFD (computational fluid dynamics) model. If you were to
model this situation using CFD, I suppose you could then take the resulting
temperature profiles and model them in EnergyPlus using USER DEFINED ROOMAIR
TEMPERATURES.
Mike
On 27 Jul 2006 at 18:07, Maria Agustin wrote:
> Hi Michael,
> Thank you for your prompt response.
> The thermal space is a central walkway between the buildings with an over
> head shading.
>
> i need to know indicative temperature profile within 1.8 metre (vertical
> height) if it si possible to maintain a space temperauture of around 24C to
> 30C during 40C and control the condensation that may occur on the exposed
> surface.
>
> the idea is to cool the slab and hopefully achieve a stratification effect
> (displacement type)that is if we can somehow control the airmovement...
>
> I have been using eQuest for a while now and learned using it the hardway, I
> did the training for energy plus in sydney sometime ago...
> I am keen to start using energy plus, however i want to get a grip on the
> software the proper way...
> I was hoping if you can guide me through...
>
> regards
> F
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> I am not sure where to start. Please give some more information
> about what you
> need to model. If this thermal zone is open to the outdoors, what is the
> control variable? This is just an open slab - no walls, no roof, no shading?
>
> Mike
>
> On 21 Jul 2006 at 20:08, Maria Agustin wrote:
>
> > I would like to model an open sky walk way using a slab cooling. The area
> is
> > arounf 200meters in lenght and 60 meters wide. CAn anyone assist me to
> start
> > cracking the simulation.
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> Send instant messages to your online friends http://au.messenger.yahoo.com
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/