[EnergyPlus_Support] Electric v/s Hot Gas Reheat
Hi All,
I am modeling a unitary system (type:Furnace:BlowThru:HeatCool)with
the high humidity control activated.
First, I run the model with a Hot Gas Reheat Coil, then with an
electric reheat coil. The rest of the model remained unchanged. The
results from the simualtion using the electric reheat coil show that
zone temperature and humidity are tightly controlled. On the other
hand, the Hot Gas reheat simulation resulted in significant zone
temperature deviations from the cooling setpoint (zone is cooled as
much as 7 oF lower that setpoint temperature, to maintain desired
max humidity). This, in turn, required a much high system cooling
capacity.
Is this real? If not, are there any other aspects of the model that
need to be modified depending on which reheat coil type is used?
Also, are there any Unitary System Objects in EnergyPlus that
support a Draw thru configuartion for cooling and BlowThru for
heating?
Your help is much appreciated.
Merid
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/