Re: [EnergyPlus_Support] Re: AHU Test



Elmer - I'll have to take a look at this when I get back from vacation 
(August 14). At least the
controllers aren't fighting each other any more

Fred

Elmer Morrissey wrote:

>Hi Fred,
>
>I made the alteration you suggested. Thank you very much.
>
>Unfortunately, the conditions off-cooling-coil are not maintained 
>100% of the time. On the 5th day, the off coil conditions creep up 
>from the 11.5C setpoint up to 14C (This is for 100% FA in a 
>London/UK climate). I cannot seem to resovle this issue.
>
>I have tried: 
>
>increasing the capacity of the cooling coil
>increasing the flowrate of chilled water
>and
>using the WaterCooling definition of cooling coil but this seems to 
>make my problems a little worse.
>
>Could you or anyone suggest anything?
>
>Kind regards
>
>-Elmer
>
>
>--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@...> 
>wrote:
>  
>
>>The Controllers on the water coils operate sequentially. In this 
>>    
>>
>case 
>  
>
>>the cooling
>>coil controller needs to go first, and the HW coil controller 
>>    
>>
>second. So 
>  
>
>>change
>>your input:
>>
>>CONTROLLER LIST,
>>    AHU1:ControlList,        !- Name
>>    Controller:Simple,       !- Controller Type 1
>>    HC:Controller,           !- Controller Name 1
>>    Controller:Simple,       !- Controller Type 2
>>    CC:Controller;           !- Controller Name 2
>>
>>to:
>>
>>CONTROLLER LIST,
>>    AHU1:ControlList,        !- Name
>>    Controller:Simple,       !- Controller Type 2
>>    CC:Controller,           !- Controller Name 2
>>    Controller:Simple,       !- Controller Type 1
>>    HC:Controller;           !- Controller Name 1
>>
>>Elmer Morrissey wrote:
>>
>>    
>>
>>>Hello all,
>>>
>>>I am having difficulty with the controls on an AHU. The AHU 
>>>      
>>>
>consists of:
>  
>
>>>Fresh Air -> Cooling Coil -> Heating Coil -> Supply Fan -> Zone
>>>
>>>The run period takes place over the first seven days in London. 
>>>      
>>>
>The
>  
>
>>>AHU is a constant volume system
>>>
>>>The cooling coil cools the air to 11.5C
>>>The heating coil heats the air back up to 16C
>>>
>>>Unfortunately, the heating coil does not engage adequately. After
>>>numerous attempts, it seems that the heating coil does not `sense'
>>>that the air has been cooled to 11.5C. The heating coil is only
>>>engaged when the outside air is below 16C (it does not realise 
>>>      
>>>
>that
>  
>
>>>the air has been cooled by the cooling coil). 
>>>
>>>I have uploaded my file to the problem submittals. It is called 
>>>      
>>>
>Test
>  
>
>>>baseboardAHU1.idf .
>>>
>>>Additional Info:
>>>
>>>All additional heating in the zone is supplemented by a baseboard
>>>heater system and the zone is maintained at 23C. As outlined
>>>previously, the system is a full fresh air constant volume system.
>>>Regardless of the outside conditions, I require the air to be 
>>>      
>>>
>cooled
>  
>
>>>to 11.5C and heated to 16C before it hits the supply fan. It is
>>>supplied directly to the zone after this.
>>>
>>>Can anyone spot how I may fix this problem?
>>>
>>>Kind regards
>>>
>>>-Elmer Morrissey
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>The primary EnergyPlus web site is found at:
>>>http://www.energyplus.gov
>>>
>>>The group web site is:
>>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>>Attachments are not allowed -- please post any files to the 
>>>      
>>>
>appropriate folder in the Files area of the Support Web Site.
>  
>
>>>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
>>>      
>>>
>and press the "search" button.
>  
>
>>>Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> 
>>>
>>>      
>>>
>
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>  
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/