The zone heat balance includes the impact of VENTILATION before computing the 
"Zone/sys sensible load to cooling setpoint predicted". The HVAC system (the 
PURCHASED AIR) sees the net load including any increase or decrease in load due 
to the VENTILATION air.  So, in answer to the specific questions:

1.  For PURCHASED AIR (with zero outside air flow in the PURCHASED AIR object), 
zone/sys cooling
energy will be reported only when the coils are on.

2.  Zone/sys sensible load to cooling setpoint predicted is the load to be 
delivered by the HVAC system.  VENTILATION objects are not considered to be 
part of the HVAC system in EnergyPlus.  So, for PURCHASED AIR this is the 
cooling coil sensible load.

3.  Correct.  The mechanical ventilation report variables only report outside 
air delivered from an HVAC system, and it only supports systems which are 
modeled with an AIR PRIMARY LOOP, not zone equipment.

4.  To achieve your goal of detemining the load due to ventilaiton air, three 
options come to mind:

a)  Do 2 runs, one with VENTILATION and one without.

b)  Report the zone/sys sensible cooling load, Zone Ventilation Sensible Heat 
Loss, and Zone Ventilation Sensible Heat Gain on an hourly basis.  Then you can 
analyze the hourly results to determine the benefits and penalties of the 
ventilation air.

c)  Use COMPACT HVAC and model a unitary system with outside air provided by 
the HVAC system.  Then the mechanical ventilation report variables will sort 
out the load impact of the outside air (cooling load increase, cooling load 
decrease, etc.) 

Mike


On 18 Aug 2006 at 12:26, Clarice Bleil de Souza wrote:

> Hi everybody,
>    
>   I am having a look at some of the EPlus outputs and would like to check
> couple of things about them.
>    
>   1) Report variable: Zone/sys sensible cooling energy 
>   
> According to the Input/output reference guide this refers to the sensible
> energy supplied by the system to the zone reporting the cooling delivered by
> the HVAC to the zone. It does not always indicate the operation of the cooling
> coil. It says that if supply air is cooled by outside air it will be reported
> as a cooling load even if the coils are off. 
>   
> On that note my question is: if I am using Purchased Air with no outside air,
> just recirculation, BUT I am defining a ventilation object the zone/sys
> cooling energy will be reported only when the coils are ON ? I ask that
> because I do have air from the outside that might be cooling the zone - as I
> specified a ventilation object - but this air is not influencing the supply
> air as it is not being mixed with the return air of the Purcahsed Air - it is
> being delivered to the zone directly. Would the zone/sys cooling energy be
> reporting a cooling load with the coils off, even if there is a ventilation
> object assigned to the zone, if the Outside air is set to "NO" in the
> purchased air object? 
>    
>   2) Report variable: Zone/sys sensible load to cooling setpoint predicted
>   
> According to the documentation this variable reports the predicted sensible
> load required to meet the setpoint. Again will this variable refers to the
> loads due to the coils ON or all the cooling loads being delivered when I
> simulate using a Purchased Air object?
>    
>   3) Report variable: Ventilation loads reports
>   
> I noticed that there are new report variables in version 1.3 refering to
> ventilation loads. I tried to use them with the same settings, Purchased air
> objects, no outside air specified for it BUT ventilation objects being used
> instead. I got null values fro all the variables refering to the ventilation
> reports. Do these reports only refer to ventilation loads when specified
> through oustide air objects? If I use the ventilation object only - even with
> mechanical ventilation sets - this variables will report me null values - is
> that correct?
>    
>   I wanted to check that because I would like to isolate cooling loads due to
> coils on from cooling loads due to ventilation only - but setting this
> ventilation separately from my ideal machine. Would this be possible in any
> way?
>    
>   Thanks a lot for the help
>    
>   Best regards, 
>    
>   Clarice
> 
> 
>  		
> ---------------------------------
>  Yahoo! Acesso Grátis - Internet rápida e grátis. Instale o discador agora! 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/