[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Heat Recovery Problems



Dear Peter

Thank you for your explaination, and I understand where the problem is now.
I will try to fix them and give you some feedbacks.
Thank you :)

mac.cz

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ellis, Peter" <peter_ellis@...> wrote:
>
>  
> The "source rate" and the "use rate" refer to the heat gain rate (or loss rate) through the 
two sets of plant loop connections to the water heater.  In your case, it sounds like you 
have the "source side" connected to the IC engine for heat recovery.  I would guess that 
your "use side" is connected to some hot water load, like domestic hot water, or maybe 
space heating.  The heat gain rate (or loss rate) for either side is calculated as the Q = 
mass flow rate * Cp * (Ttank - Tinlet).  
>  
> That said, it is not often the case that the source rate and the use rate will match each 
other.  That is usually why the water heater has some volume to it for energy storage, and 
why there's a burner or electric heating element to provide auxiliary heat when necessary.  
If your water heater has an auxiliary heat source, you need to take that into account too.  
The report variable for that is "Water Heater Heating Rate".  You may also have parasitics 
adding extra heat to your water heater also.  
>  
> Finally, keep in mind that the heat rates will only add up if the water heater is kept at a 
steady-state temperature.  If, for example, you do not have a burner on your water heater 
and the use rate is greater than the source rate, the water in the tank will cool down until 
there's no more useable energy left.  Or conversely, if you are adding more heat through 
the source side than you are using, the tank temperature will heat up until it hits the 
Maximum Temperature Limit at which point the heat is vented away and lost.  
>  
> As for the IC engine heat recovery, you should be able to verify the actual heat recovery 
rate delivered by the plant loop by looking at the mass flow rate through the IC engine, the 
inlet water temperature and the outlet water temperature.  This calculation should match 
the water heater source rate.  There may be some reason why the "total heat recovery rate" 
of the IC engine is defined differently, I don't know.  Hopefully, they match.  
>  
> If this hasn't explained your problem yet, you can post the file.
>  
>  
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx 
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of energypluser
> Sent: Sunday, September 03, 2006 3:19 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Heat Recovery Problems
> 
> 
> 
> Dear all
> 
> I connected a water heater to an IC engine for the purpose of recovering the exhausted 
heat.
> When I was checking the results, I found something that I can not understand.
> First, I found that the source rate of the water heater is much larger than the use rate. 
The 
> difference is around 12kW in the winter design day and 7kW in the summer design day.
> I checked that the heat loss rate is around 0.3kW in design days.
> Why are some heat missing?
> Second, I found that the total heat recovery rate of the IC engine was around 28kW in 
the 
> design days. It is bigger than the source rate of the water heater! So the same problem 
> appears again: there are some heat missing.
> How can I explain this kind of things?
> Thank you in advance!
> 
> mac.cz
> 
> 
> 
>  
> 
> 
> [Non-text portions of this message have been removed]
>







The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/