Peter, let me thank you right now for your mails.
Andrea.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ellis, Peter" 
<peter_ellis@...> wrote:
>
>  
> Just to follow up, I now have been able to confirm that with the 
changes below, the input file DOES demonstrate a correct energy 
balance on the water heater.  I think the SYSTEM CONVERGENCE LIMITS 
had a lot to do with the trouble you might have been seeing.  
>  
> Some tips on verifying the energy balance:  
>  
> 1.  Use the new report variable in V 1.4 called "Water Heater 
Final Tank Temperature" to find the final tank temperature at the 
end of the timestep, otherwise you get an average over the 
timestep.  This is what you'll use to measure the actual change in 
energy in the tank.  
>  
> 2.  Report your variables at the "timestep" interval instead 
of "hourly".  Tank temperatures can change rapidly within an hour.  
The hourly values are averages of the timestep values and therefore 
will not be as accurate for checking the energy balance...that is 
assuming that your timestep is less than 1 hour.  
>  
> 3.  The minor bug that I mentioned below pertains to the reporting 
of the variable "Water Heater Net Heat Tranfer Energy".  I think 
the "Vent" energy is getting added into this with the wrong sign.  
When in doubt, manually add up the components for "loss 
energy", "use energy", "source energy", and "vent energy".  
>  
> Let me know if you have any further questions.
>  
> P
>  
>  
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx 
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]On Behalf Of Ellis, Peter
> Sent: Thursday, October 26, 2006 4:43 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: RE: [EnergyPlus_Support] Re: Heat Recovery Problems
> 
> 
> 
> 
> Hi Andrea,
> 
> I just wanted to let you know I have been looking at your input 
file. So far I have found a couple of things that will need to be 
fixed in your file before it will run properly. 
> 
> 1. You have SYSTEM CONVERGENCE LIMITS set as follows:
> 
> System Convergence Limits,
> 60, !- Minimum System Time Step {minutes}
> 2000; !- Maximum HVAC Iterations
> 
> The default "Minimum System Time Step" is 1 minute. 60 minutes 
means that the system is simulated AT MOST once per hour. This is 
giving some really strange results. I don't think the system 
simulation is completing correctly with this setting. (At least it 
is not greater than your timestep of 1 hour.) I would suggest 
leaving it at the default of 1 minute unless you have a good reason 
for doing otherwise. 
> 
> 2. You have TIMESTEP IN HOUR set to 1. This is not too bad, but 
usually the plant simulation will run better at 4 or 6 
timesteps/hour. The problem is that the plant loop volume becomes 
very large at 1 hour timesteps. To account for the thermal mass in 
the loop you end up getting a very large temperature jump between 
the outlet of the demand side and the inlet of the supply side (or 
is it vice versa? I forget.) Once you are convinced that everything 
is running correctly, then you might try experimenting with a 1 hour 
timestep. 
> 
> 3. Don't forget Sankar's observation that you want the water 
heater branch to be ACTIVE:
> 
> BRANCH,
> Water Heater Use Branch, !- Branch Name
> 0, !- Maximum Branch Flow Rate {m3/s}
> WATER HEATER:MIXED, !- Comp1 Type
> Water Heater, !- Comp1 Name
> Water Heater Use Inlet Node, !- Comp1 Inlet Node Name
> Water Heater Use Outlet Node, !- Comp1 Outlet Node Name
> ACTIVE; !- Comp1 Branch Control Type
> 
> 4. Your second water heater "secondo boiler" does not have any 
heating capacity. So it is not doing any auxiliary heating and you 
are probably not getting the space heating that you hope for at all 
times. 
> 
> 
> There may still be an energy imbalance that you've found here, but 
I'm not sure yet. There is at least one minor bug in the reporting 
for the net heat transfer that I've found, but that should not cause 
any energy imbalance. I will continue my investigation and let you 
know as soon as I have a definite answer. I do, however, want to 
point out that the energy balance on the SolarCollectorFlatPlate.idf 
file was corrected with the new release (I just double-checked). So 
if there is an energy imbalance in your new file, then this is a new 
bug! 
> 
> Peter
> 
> 
> 
> -----Original Message-----
> From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%
40yahoogroups.com> yahoogroups.com [mailto: EnergyPlus_Support@ 
<mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com]On 
Behalf Of ingdallolio
> Sent: Tuesday, October 24, 2006 12:32 AM
> To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%
40yahoogroups.com> yahoogroups.com
> Subject: [EnergyPlus_Support] Re: Heat Recovery Problems
> 
> Peter, 
> If I understand correctly, your water heater is still too 
generous !
> The energy is still not balancing in waterheater E+ v 1.4 ? 
> As usual, thank you and the E+ team for your work.
> Andrea.
> 
> --- In EnergyPlus_Support@ <mailto:EnergyPlus_Support%
40yahoogroups.com> yahoogroups.com, "Ellis, Peter"
> <peter_ellis@> wrote:
> >
> > 
> > The energy numbers are actually correct for any given time step
> because they are based solely on the tank temperature at that time
> step and the various energy flows into and out of the tank. In 
other
> words there is a correct energy balance at the time step level. 
> Unfortunately, the problem is with the thermal history of the
> tank--the tank temperature is not propagating correctly from time 
step
> to time step. It's actually moving ahead in time about 4 times as
> fast as it should. That means the tank temperatures are wrong, and 
by
> extension the energy numbers are wrong too. Ultimately, this messes
> up the energy balance at longer time scales, e.g., over a day or a
> year. So to sum up, both the outputs and actual performance are
> incorrect. 
> > 
> > Peter
> > 
> > 
> > -----Original Message-----
> > From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%
40yahoogroups.com> yahoogroups.com
> [mailto: EnergyPlus_Support@ <mailto:EnergyPlus_Support%
40yahoogroups.com> yahoogroups.com]On Behalf Of ingdallolio
> > Sent: Thursday, September 21, 2006 11:00 AM
> > To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%
40yahoogroups.com> yahoogroups.com
> > Subject: [EnergyPlus_Support] Re: Heat Recovery Problems
> > 
> > 
> > 
> > Thank you and the team for the work Peter.
> > 
> > One more question, is the problem just on energy output numbers 
or is
> > it effecting the component actual performance? I mean, beside the
> > energy output values, are the other output of the model still 
good ?
> > 
> > Andrea.
> > 
> > --- In EnergyPlus_Support@
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
yahoogroups.com, "Ellis,
> Peter"
> > <peter_ellis@> wrote:
> > >
> > > 
> > > Andrea,
> > > I have confirmed that there is indeed a bug with the water 
heater
> > object. The thermal history of the tank is being incorrectly 
updated
> > several times per system time step (should be only once per sys 
time
> > step). This is causing the problems in the energy balance that 
you
> > were seeing. Originally the water heater did have the correct 
energy
> > balance. This bug was most likely introduced one or two releases 
ago.
> > Although we do extensive testing to try to make sure that we 
don't
> > "break" anything from release to release, this bug got by us 
somehow. 
> > > 
> > > The bug has now been fixed. You should be able to successfully
> > confirm the energy balance in the upcoming release in October. I 
have
> > also added a new report variable for the water heater that gives 
you
> > the final tank temperature at the end of the time step. This 
should
> > allow you to show an exact energy balance between the tank 
starting
> > conditions and ending conditions and the various fluid flows. 
> > > 
> > > Thanks for your persistence and patience in dealing with this 
bug.
> > > 
> > > Peter Ellis
> > > National Renewable Energy Laboratory
> > > 
> > > 
> > > -----Original Message-----
> > > From: EnergyPlus_Support@
> <mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com
> > [mailto: EnergyPlus_Support@
> <mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com]On
> Behalf Of ingdallolio
> > > Sent: Tuesday, September 05, 2006 3:22 PM
> > > To: EnergyPlus_Support@
> <mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com
> > > Subject: [EnergyPlus_Support] Re: Heat Recovery Problems
> > > 
> > > 
> > > 
> > > Peter,
> > > I understand source and use power do not match in a water 
heater but
> > > energy source and use should balance in a year period ( with 
stored
> > > heat and losses of course ), they do not match in any water 
heater I 
> > > tried like the example file collectorflatplate.idf.
> > > Mike Wite confirmed me the unbalance before summer but so far 
no info
> > > about the issue nor it's in the known issue list. The present 
version
> > > waterheater object can be considered reliable ?
> > > Grazie (Thanks).
> > > Andrea. 
> > > 
> > > I've also problem in balancing energy 
> > > 
> > > --- In EnergyPlus_Support@
> > <mailto:EnergyPlus_Support%40yahoogroups.com> 
yahoogroups.com, "Ellis,
> > Peter"
> > > <peter_ellis@> wrote:
> > > >
> > > > 
> > > > The "source rate" and the "use rate" refer to the heat gain 
rate (or
> > > loss rate) through the two sets of plant loop connections to 
the water
> > > heater. In your case, it sounds like you have the "source side"
> > > connected to the IC engine for heat recovery. I would guess 
that your
> > > "use side" is connected to some hot water load, like domestic 
hot
> > > water, or maybe space heating. The heat gain rate (or loss 
rate) for
> > > either side is calculated as the Q = mass flow rate * Cp * 
(Ttank -
> > > Tinlet). 
> > > > 
> > > > That said, it is not often the case that the source rate and 
the use
> > > rate will match each other. That is usually why the water 
heater has
> > > some volume to it for energy storage, and why there's a burner 
or
> > > electric heating element to provide auxiliary heat when 
necessary. If
> > > your water heater has an auxiliary heat source, you need to 
take that
> > > into account too. The report variable for that is "Water Heater
> > > Heating Rate". You may also have parasitics adding extra heat 
to your
> > > water heater also. 
> > > > 
> > > > Finally, keep in mind that the heat rates will only add up 
if the
> > > water heater is kept at a steady-state temperature. If, for 
example,
> > > you do not have a burner on your water heater and the use rate 
is
> > > greater than the source rate, the water in the tank will cool 
down
> > > until there's no more useable energy left. Or conversely, if 
you are
> > > adding more heat through the source side than you are using, 
the tank
> > > temperature will heat up until it hits the Maximum Temperature 
Limit
> > > at which point the heat is vented away and lost. 
> > > > 
> > > > As for the IC engine heat recovery, you should be able to 
verify the
> > > actual heat recovery rate delivered by the plant loop by 
looking at
> > > the mass flow rate through the IC engine, the inlet water 
temperature
> > > and the outlet water temperature. This calculation should 
match the
> > > water heater source rate. There may be some reason why 
the "total
> > > heat recovery rate" of the IC engine is defined differently, I 
don't
> > > know. Hopefully, they match. 
> > > > 
> > > > If this hasn't explained your problem yet, you can post the 
file.
> > > > 
> > > > 
> > > > -----Original Message-----
> > > > From: EnergyPlus_Support@
> > <mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com
> > > [mailto: EnergyPlus_Support@
> > <mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com]On
> > Behalf Of energypluser
> > > > Sent: Sunday, September 03, 2006 3:19 AM
> > > > To: EnergyPlus_Support@
> > <mailto:EnergyPlus_Support%40yahoogroups.com> yahoogroups.com
> > > > Subject: [EnergyPlus_Support] Heat Recovery Problems
> > > > 
> > > > 
> > > > 
> > > > Dear all
> > > > 
> > > > I connected a water heater to an IC engine for the purpose of
> > > recovering the exhausted heat.
> > > > When I was checking the results, I found something that I 
can not
> > > understand.
> > > > First, I found that the source rate of the water heater is 
much
> > > larger than the use rate. The 
> > > > difference is around 12kW in the winter design day and 7kW 
in the
> > > summer design day.
> > > > I checked that the heat loss rate is around 0.3kW in design 
days.
> > > > Why are some heat missing?
> > > > Second, I found that the total heat recovery rate of the IC 
engine
> > > was around 28kW in the 
> > > > design days. It is bigger than the source rate of the water 
heater!
> > > So the same problem 
> > > > appears again: there are some heat missing.
> > > > How can I explain this kind of things?
> > > > Thank you in advance!
> > > > 
> > > > mac.cz
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > > [Non-text portions of this message have been removed]
> > > >
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > [Non-text portions of this message have been removed]
> > >
> > 
> > 
> > 
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> >
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
>  
> 
> 
> [Non-text portions of this message have been removed]
>





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/