Well, I see that the daylighting section of the Input Output Reference is
inconsistent on these subjects. (On the list to fix now.)
Referring to p. 290 of the I/O Reference (pdf p. 327), internal obstructions
accounted for in daylighting. This is not mentioned in the list of differences
for DElight, so I assume that DElight also accounts for internal obstructions.
I cannot say that I have verified this for either of the daylighting models.
For solar gains, interior obstructions are not accounted for. The FullInterior
solar distribution options require a "convex" zone. From p. 12 (pdf p. 49) "A
formal definition of convex is that any straight line passing through
the zone intercepts at most two surfaces.)"
Mike
On 8 Sep 2006 at 11:04, Andy Tindale wrote:
> Mike,
>
> Is it possible to use EnergyPlus to model large internal obstructions to
> solar and daylighting penetration within a zone using surfaces or other
> objects?.
>
> Clearly this would require the full exterior and interior solar distribution
> option, but I just wondered whether the presence of any internal obstruction
> surfaces would be accounted for in the calculation of daylight factors and
> solar distribution about the space. Are Daylighting:Detailed and
> Daylighting:DELight the same in this respect.
>
> Thanks,
>
> Andy
>
> Andy Tindale
> DesignBuilder Software Limited
> Email: andy@xxxxxxxxxxxxxxxxxxx
> website: http://www.designbuilder.co.uk
>
> DISCLAIMER:
> This message is confidential. You should not copy it or disclose its
> contents to anyone. You may use and apply the following only for the
> intended purpose. Internet communications are not secure and therefore
> DesignBuilder Software Limited does not accept legal responsibility for the
> contents of this message. Any views or opinions presented are only those of
> the author and not those of DesignBuilder Software Ltd. If this email has
> come to you in error please delete it and any attachments.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/