Regarding daylight (visible light) interreflections within a zone, the
Detailed method uses a split-flux method, whereas DElight uses a
modified radiosity method. The split-flux method divides transmitted
daylight into "downward-going" and "upward-going" fluxes and evenly
distributes a portion of these fluxes as reflected light based on an
area-weighted average surface reflectance for the zone. See the
Engineering Documentation page 116 (PDF page 148) for more detail. This
method does not accurately account for interior obstructions in the
interreflection calculation. The radiosity method more accurately
accounts for interreflection between interior surfaces by discretizing
each surface into nodal patch areas and accounting for the reflective
exchange of visible light between the patch areas.
Regarding direct daylight distribution (i.e., exterior light directly
reaching reference points and interior surfaces through apertures), the
Detailed method does account for the obstruction, by the interior face
of zone surfaces, of direct daylight on reference points (but not on
interior surfaces), while the DElight method currently does not,
assuming zones are convex, as Mike describes below for solar gains.
Rob Hitchcock
==========
Michael J. Witte wrote:
> Well, I see that the daylighting section of the Input Output Reference is
> inconsistent on these subjects. (On the list to fix now.)
>
> Referring to p. 290 of the I/O Reference (pdf p. 327), internal
> obstructions
> accounted for in daylighting. This is not mentioned in the list of
> differences
> for DElight, so I assume that DElight also accounts for internal
> obstructions.
> I cannot say that I have verified this for either of the daylighting
> models.
>
> For solar gains, interior obstructions are not accounted for. The
> FullInterior
> solar distribution options require a "convex" zone. From p. 12 (pdf p.
> 49) "A
> formal definition of convex is that any straight line passing through
> the zone intercepts at most two surfaces.)"
>
> Mike
>
> On 8 Sep 2006 at 11:04, Andy Tindale wrote:
>
> > Mike,
> >
> > Is it possible to use EnergyPlus to model large internal obstructions to
> > solar and daylighting penetration within a zone using surfaces or other
> > objects?.
> >
> > Clearly this would require the full exterior and interior solar
> distribution
> > option, but I just wondered whether the presence of any internal
> obstruction
> > surfaces would be accounted for in the calculation of daylight
> factors and
> > solar distribution about the space. Are Daylighting:Detailed and
> > Daylighting:DELight the same in this respect.
> >
> > Thanks,
> >
> > Andy
> >
> > Andy Tindale
> > DesignBuilder Software Limited
> > Email: andy@xxxxxxxxxxxxxxxxxxx <mailto:andy%40designbuilder.co.uk>
> > website: http://www.designbuilder.co.uk <http://www.designbuilder.co.uk>
> >
> > DISCLAIMER:
> > This message is confidential. You should not copy it or disclose its
> > contents to anyone. You may use and apply the following only for the
> > intended purpose. Internet communications are not secure and therefore
> > DesignBuilder Software Limited does not accept legal responsibility
> for the
> > contents of this message. Any views or opinions presented are only
> those of
> > the author and not those of DesignBuilder Software Ltd. If this
> email has
> > come to you in error please delete it and any attachments.
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov <http://www.energyplus.gov>
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/>
> >
> > Attachments are not allowed -- please post any files to the
> appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
> press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com>
>
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/