[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Plant Loop Setting
Dear Michael,
I posted my files in EPSupport_BaseboardModel.zip and with the
explanation "Baseboar Heater Model and Plant Loop Control". I could
not find where is the wrong in my files. I am sending to you three
files *.idf, all of them more or less similar. In addition I am
sending to you a doc file, with the explanation what about I am
wondering.
Please, help to me with your answer or adivece.
Thank you in advance!
Natasa M.Djuric
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> 1. Baseboard Heater:Water:Convective is intended to model
thermostatically
> controlled baseboard heat. The model is not controlling return
water
> temperature, rather it is controlling the water flow rate to add
the required
> amount of heat to the zone to meet the thermostat setpoint. There
is not a
> direct way to model uncontrolled baseboard with varying supply
temperature.
> The way to make the baseboard always run at full flow is to set
the thermostat
> setting very high. You should then see full flow whenever the
system is on,
> but the heat output and suppy-return deltaT should vary as the
supply
> temperature varies.
>
> 2. Check the setpoint schedule definition. There should be no
difference in
> setpoint operation between design days and other days. If you
cannot see the
> problem in the schedule definition, then please sumbit the file
(zipped) to the
> files are of the yahoo group or e-mail to energyplus-support@...
>
> Mike
>
>
> On 19 Sep 2006 at 12:37, natasamdj wrote:
>
> > Dear,
> > I have two questions about the Plant Loop settings. I have made
a
> > model with the Baseboard Heater: Water: Convective. In addition
I
> > have the real data, and I would like to adjust the simulation
output
> > with these real-life data.
> > 1. I set the Loop Temperature Setpoint by using Set Point
Manager:
> > Outside Air. I found out in the output that E+ calculated the
load
> > so that water mass flow rate has been increased how the Loop
> > Temperature is lower. In other words, how the outdoor
temperature
> > increases, the supply water temperature is decreased, and the
water
> > flow is increased. I have some real data, and I would like to
> > combine that with the simulation results. Actually, I found out
that
> > E+ calculated almost the same return temperature for the
different
> > outdoor temperatures, while the supply temperature is decreased.
> > Because of that the water flow has been increased all the time
how
> > the outdoor temperature is increased. How I can model different
> > managing of the return temperature? Is it possible to model that
the
> > difference between the supply and return water temperature is
> > constant (or almost) constant for the different outdoor
conditions?
> > 2. I found in the report output, that System Node Setpoint Temp
for
> > the demand side is calculated only for the design day, while for
the
> > other days it is zero (0). In this case the System Node Setpoint
> > Temp for Demand side should be calculated regarding to Set Point
> > Manager: Outside Air, and it is calculated exactly by this
schema
> > but only for the design day. In addition, the System Node
Setpoint
> > Temp is calculated correctly for all the nodes at Supply side,
but
> > not for the nodes at Demand side. What should I do to get these
> > temperatures correctly for all other days at Demand side nodes?
> >
> > If it is necessary I can send to my *.idf file.
> >
> > Thank you in advance!
> >
> > Natasa M.Djuric
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/