[EnergyPlus_Support] other questions about plant-loop and condenser -loop.
Hi Mike,
Thank you very much!you are so kind!
1.I want to see the optimum control of plant loop.so i set 2 branches
with branch-pumps.and i set the bypass branches both in supply side
and demand side.but there are always warnings:
** Warning ** Error -- Mass Flow Rate Calculation in Plant Loop=HW-1-
LOOP, Outlet and Inlet differ by more than tolerance.
** ~~~ ** Occurrence info=WINTER-DESIGN-DAY, 01/21 08:00 -
09:00
** ~~~ ** Loop inlet node=HW-1-SS-IN-PIPE-IN-ND,
flowrate=8.0905 m/s
** ~~~ ** Loop outlet node=HW-1-SS-OUT-PIPE-OUT-ND,
flowrate=16.1811 m/s
What should i do?
2.it's not convenient for condenser-loop only could be set a circle-
pump per loop.so for two chillers,one condenser-pump is not
physical,and just one pump is not energy-save.
how to solve that problem? set two condenser-loops for different
chillers?
Well Kong
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> It is difficult to say for sure without seeing the input file.
This type of
> error usually occurs when the loop is unable to conserve mass flow
around the
> loop. Check the flow rates specified for the cooling tower(s) and
the
> condenser loop pump and in the condenser loop object. Check if
there is a
> bypass. Check the pump controls. Check the ACTIVE/PASSIVE
settings on the
> branches. See ExampleFiles\CoolingTower.idf for an example.
>
> Mike
>
>
> On 25 Sep 2006 at 5:25, well_kong wrote:
>
> > I simulated whole IDF file.and it's warning so many times!
> > I really can't resolve it.
> > Why the minimum mass flow is greater than the maximum?
> >
> > ** Warning ** COOLING TOWER:SINGLE SPEED- "CT-SS-TOWER-1":
> > ** ~~~ ** Condenser Minimum Loop Mass Flow is greater
than
> > Condenser Maximum Loop Mass Flow
> > ** ~~~ ** Minimum Loop Mass Flow has been reset to
Maximum Loop
> > Mass Flow
> >
> >
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf
and press the
> > "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/