Re: [EnergyPlus_Support] Using SCHEDULE:FILE:COMMA
>From your input file it appears that you are still using 1.2.3. There was a
bug in SCHEDULE:FILE:COMMA in version 1.2.3 when "rows to skip"=0. The
workaround is to add an extra row at the top of the file and set the "rows to
skip" to 1 or more. An even better solution is to upgrade to version 1.3.0 :-)
Mike
On 26 Sep 2006 at 12:28, natasamdj wrote:
> Dear,
> Before some days some of you from Support Group recomended to me for
> using SCHEDULE:FILE:COMMA. I have applied it. But E+ error file
> writes me always a message "less than 8760 hourly values". In my txt
> file for the schedule I have even more then 8760 values. Of course I
> tested with 8760 values, but I get the same message. Is there some
> special protocol how I should write the values in the *.txt file? I
> wrote as it is explained in the E+ help, in each line one value for
> each hour with the comma as a separator. I have written only one
> value for each hour and the same value for the whole year. Actually
> my aim was to test that option. Maybe I made some wrong, but can you
> help me how I should do it. I have attached a few of my files
> together with this txt file in EPSupport_BaseboardModel.zip with the
> explanation Baseboar Heater Model and Plant Loop Control.
> I have one question more about using this schedule option. Is it
> possible to get some of the data from this schedule file as the
> output report variables, even if that data is not processed trough
> E+? If it is possible how it should be specified in the report
> variable?
>
> Thank you in advance!
>
> Natasa M.Djuric
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/