Re: [EnergyPlus_Support] SimHVAC Max Iterations Exceeded - Exh Fan?
There are a couple of problems in this input file that should concern you:
1) Loads Initialization does not converge.
I took out the system from the input file and this problem went
away -- this would imply that the problem is in the system definition
and the zone temperatures keep getting warmer and warmer (or colder
and colder) and not converging.
2) Unbalanced exhaust flow. This is not too concerning, but you
should check to make sure the exhaust fan is turned off when the
system in turned off -- this error most often happens when the
exhaust fan is running but there is no supply air.
It is possible once you correct #1 that the max iterations will go
away. You also have an hourly time step here -- we suggest a time
step of 10 minutes for those input files with systems. Also, you
have specified a minimum system convergence -- it might be better
until you are certain of things to allow these to default.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/