Not exactly, you'll need separate People objects with unique names for
each zone. (I just use the zone name as part of the name to get unique
names.)
If your zones are really uniform (same sizes, internal gains,
orientation, etc.), then you could go another even simpler route which
is to use zone multipliers. This way you define a single zone just one
time and then give it a zone multiplier. The resulting loads will be
amplified by the multiplier.
brent
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of asheaffe
Sent: Tuesday, October 10, 2006 2:09 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Loads question
If I have several zones which are going to have the same loads (ie
similar sized zones with exactly the same number of people in each, on
the same schedule, etc.) is there any way that I can assign multiple
zones to one load definition object? For example, is there any way
for me to set up a standard load of 10 people in a zone with a
specific schedule and just have each zone reference this object? I am
trying to avoid having to come up with unique names for each load
object.
Thanks,
andrew
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/