Those are good questions.  The zone multiplier is applied when loads are passed 
to the HVAC system and when energy use is metered.  For the energy meters, you 
can see in the MTD file where the multipliers have been applied.  For example:

 Meters for 5037,PER-1I LIGHTS 1:Lights Electric Consumption [J] * 4  (Zone 
Mult = 4, Zone List Mult = 1)

In general, zone-level objects, such as lights, people, infiltration should not 
be multiplied upon input and will not be multiplied upon output.  Only HVAC 
output and meter output is multiplied.  So, you do not need to multiply the 
infiltration values.  And the window heat gain should be the unmultiplied 
value.  But I would recommend changing the multiplier and confirming that the 
window heat gain does not change.

Mike


On 16 Oct 2006 at 20:09, kir kumar wrote:

> Dear all,
>        I simulated a huge building with seven floors . Each floor has two
> zones. I used zone multiplier to multiply my middle floor by 5 times.Do I need
> to divide every resulting value for middle floor by 5 in order to attain a
> value just for a typical middle floor?
>      
>        For example Do I need to divide the resulting cooling loads of  middle
> floor by 5, to get the cooling load of typical middle floor?. Also do I need
> to divide the resulting value by 5 in order to get the middle floor window
> heat gain?
>    
>        How about infiltration? Do I need to input infiltration values just for
> a typical middle floor assuming that E+ automatically multiplies the given
> infiltration value by 5 times. or Do I need to input an infiltration value
> five times that of a typical middle floor?
>    Can any one help me answere my questions?
>   thanks in advance
>   kiran
> 
>  				
> ---------------------------------
>  Find out what India is talking about on  - Yahoo! Answers India 
>  Send FREE SMS to your friend's mobile from Yahoo! Messenger Version 8. Get it
> NOW
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/