Re: [EnergyPlus_Support] Unitary equipment
To model a unitary VAV system, it would be easiest to start with COMPACT
HVAC:*:VAV objects and skip the plant loops. Run this (EnergyPlus will fail,
but that's OK) and take the resulting expidf file and make the following
changes:
1. In the main branch of the air loop, put in a DXSystem:AirLoop instead of
the chilled water coil.
2. Delete the chilled water cooling coil object and its branch and controller,
and delete the controller from the controller list.
3. Add a DXSystem:AirLoop and COIL:DX:MultiSpeed:CoolingEmpirical and related
objects.
That should do it. Use example file 5ZoneAutoDXVAV.idf as a guide.
Mike
On 19 Oct 2006 at 20:25, asheaffe wrote:
> Is there any way to convert a compact HVAC unitary system to a VAV
> system? I'd really like to simplify my input process by using this
> compact object, but I want to specify a VAV.
>
> Thanks,
>
> Andrew
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/