[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Detailed Cooling Coil Fatal Error
Dear all,
I'm using the detailed cooling coil for a simulation. However I get
the following warning which leads to a fatal error
** Warning ** Calculated design heating load for zone=TESTZONE is zero.
** ~~~ ** Check ZONE SIZING and ZONE CONTROL:THERMOSTATIC inputs.
************* Beginning System Sizing Calculations
************* Beginning Plant Sizing Calculations
** Severe ** InitWaterCoil: Detailed Flat Fin Coil,
TubetoFinDiamRatio > 1.0, [2.2856]
The input for the run looks as follows:
COIL:Water:DetailedFlatCooling,
AHU2 CC, !- Coil Name
PlantAvailSched, !- Available Schedule
0.006646, !- Max Water Flow Rate of Coil {m3/s}
autosize, !- Tube Outside Surf Area {m2}
autosize, !- Total Tube Inside Area {m2}
autosize, !- Fin Surface Area {m2}
autosize, !- Minimum Air Flow Area {m2}
autosize, !- Coil Depth {m}
autosize, !- Fin Diameter {m}
0.0015, !- Fin Thickness {m}
0.01445, !- Tube Inside Diameter {m}
0.0159, !- Tube Outside Diameter {m}
0.386, !- Tube Thermal Conductivity {W/m-K}
0.204, !- Fin Thermal Conductivity {W/m-K}
0.0018, !- Fin Spacing {m}
0.026, !- Tube Depth Spacing {m}
4, !- Number of Tube Rows
autosize, !- Number of Tubes per Row
CW:CC:WaterInletNode, !- Coil_Water_Inlet_Node
CW:CC:WaterOutletNode, !- Coil_Water_Outlet_Node
AirNode4, !- Coil_Air_Inlet_Node
AirNode5; !- Coil_Air_Outlet_Node
As you can see, the input is taken from the default settings with the
object with 90% of the fields being autosized. Does anyone have any
thoughts?
Kind regards
-Elmer
PS the autosizing parameters:
ZONE SIZING,
TestZone, !- Name of a zone
11.5, !- Zone cooling design supply air
temperature {C}
16.5, !- Zone heating design supply air
temperature {C}
0.0065, !- Zone cooling design supply air
humidity ratio {kg-H2O/kg-air}
0.0065, !- Zone heating design supply air
humidity ratio {kg-H2O/kg-air}
flow/person, !- outside air method
0.00944, !- outside air flow per person {m3/s}
, !- outside air flow per zone {m3/s}
1, !- zone sizing factor
design day, !- cooling design air flow method
, !- cooling design air flow rate {m3/s}
design day, !- heating design air flow method
; !- heating design air flow rate {m3/s}
!- =========== ALL OBJECTS IN CLASS: SYSTEM SIZING ===========
SYSTEM SIZING,
AHU2:PrimaryAirLoop, !- name of an AIR PRIMARY LOOP object
sensible, !- type of load to size on
6, !- Design (minimum) outside air
volumetric flow rate {m3/s}
1, !- minimum system air flow ratio
4, !- Preheat design set temperature {C}
11.5, !- Central cooling design supply air
temperature {C}
16.5, !- Central heating design supply air
temperature {C}
noncoincident, !- Sizing Option
no, !- Cooling 100% Outside Air
no, !- Heating 100% Outside Air
0.0065, !- Central cooling design supply air
humidity ratio {kg-H2O/kg-air}
0.0065, !- Central heating design supply air
humidity ratio {kg-H2O/kg-air}
design day, !- cooling design air flow method
, !- cooling design air flow rate {m3/s}
design day, !- heating design air flow method
; !- heating design air flow rate {m3/s}
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/