[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Fanger Comfort
Dear Brent,
I see only the Fanger PMV in the last column of the comfort tables.
How do I
(1) use objects like People object (Fanger, Pierce and KSU)
(2) use the Fanger model directly?
Sincerely,
Ooi
_____
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Griffith, Brent
Sent: Tuesday, October 24, 2006 12:03 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Fanger Comfort
EnergyPlus offers many different ways to report occupant comfort. In
addition to the ASHRAE 55 report variables, there are three different
comfort models available through the People object (Fanger, Pierce,
KSU). I think the ASHRAE 55 summer/winter ranges are derived from using
the Fanger model with different clothing levels for summer or winter.
If you use the Fanger model directly then you have full control over the
amount of clothing by scheduling for the levels for "clo."
________________________________
From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
[mailto:EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com] On Behalf Of kooi
Sent: Saturday, October 21, 2006 3:56 AM
To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
Subject: RE: [EnergyPlus_Support] Fanger Comfort
Dear Mike or Linda or Brent,
The ASHRAE Standard 55 comfort has different ranges (in humidity and
temperature) for Winter and Summer. Correct me if I am wrong, this is
used
programmed into EnergyPlus to show (in the output files) when occupants
are
comfortable or not.
How about a tropical country where there is no Winter or Summer? I would
like to classify that the occupants are comfortable only in the range
overlapped by the ASHRAE 55 Winter and Summer. Presuming that the second
sentence in the first para is not wrong, what changes do I have to make
to
output results with this new definition of comfort.
Thank you
ooi
_____
From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
<mailto:EnergyPlus_Support%40yahoogroups.com>
[mailto:EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
<mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of Griffith,
Brent
Sent: Saturday, October 21, 2006 5:05 AM
To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
<mailto:EnergyPlus_Support%40yahoogroups.com>
Subject: RE: [EnergyPlus_Support] Fanger Comfort
Yes, the Fanger Calculations have been compared to ASHRAE Comfort Tool
and Appendix D of ASHRAE Standard 55.
The most common problems I see in EnergyPlus runs that seem to show poor
PMV results are the following:
1. the HVAC system is missing or isn't actually controlling zone
conditions as expected
2. wrong or poor values for the schedules for activity level, air
velocity, or clo
3. the relative humidity can come out unusually low in the winter.
4. the heat balance model does a good job of predicting inside face
surface temperatures, but this can lead to some surprising results in
PMV that stem from the radiant temperature terms.
I find the following input object helpful for such issues.
Report:Table:Monthly,
Occupant Comfort Data Summary, !- Name
3, !- DigitsAfterDecimal
People Number of Occupants, !- VariableOrMeterName01
HoursNonZero, !- AggregationType01
Zone/Sys Air Temperature, !- VariableOrMeterName02
SumOrAverageDuringHoursShown, !- AggregationType02
Zone Air Relative Humidity, !- VariableOrMeterName03
SumOrAverageDuringHoursShown, !- AggregationType03
ThermalComfortMRT,
SumOrAverageDuringHoursShown, !- AggregationType03
Time Not Comfortable Summer Or Winter Clothes,
SumOrAverageDuringHoursShown,
FANGERPMV, !- VariableOrMeterName04
SumOrAverageDuringHoursShown; !- AggregationType04
________________________________
From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
[mailto:EnergyPlus_Support@
<mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com] On Behalf Of Ian Doebber
Sent: Friday, October 20, 2006 2:24 PM
To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
Subject: [EnergyPlus_Support] Fanger Comfort
Has the Fanger comfort model been fixed in the V1.3 release and compares
to the calculation from the ASHRAE Comfort model. This was an error
that was highlighted months ago. Let me know.
Thanks in advance
Ian Doebber
Graduate Mechanical Engineer
Arup
901 Market Street Suite 260 San Francisco CA 94103
tel: 415-946-0292
fax: 415-957-9096
cell: 415-613-4314
ian.doebber@ <mailto:ian.doebber%40arup.com> arup.com
<mailto:ian.doebber%40arup.com>
www.arup.com
________________________________
From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
<mailto:EnergyPlus_Support%40yahoogroups.com>
[mailto:EnergyPlus_Support@
<mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
<mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of Michael J.
Witte
Sent: Thursday, October 19, 2006 11:38 AM
To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
<mailto:EnergyPlus_Support%40yahoogroups.com>
Subject: RE: [EnergyPlus_Support] Further Insight : Skylight / Radiant
Cooling Strange Behavior
Ian:
If you delete the skylights, does the cooling load on the radiant system
change
by the same order of magnitude as the reported heat gain from the
skylights? I
suspect this may just be a problem with the reported window heat gain
rather
than a real heat balance problem. The reported window heat gain is just
a side
calculation for reporting purposes, that value is not actually used in
the heat
balance.
Mike
On 15 Oct 2006 at 15:42, Linda Lawrie wrote:
> At 04:27 PM 10/13/2006, Griffith, Brent wrote:
> >I believe this is a known bug (CR6897). But unfortunately it isn't a
> >quick job and I don't think it was fixed in V1.4 (which is already
out).
>
> As Brent says, this is a known or suspected problem. If you submit
> your file (either send direct to me or upload to the support web
> site), it may help our developer in tracking it down.
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energypl <http://www.energypl
<http://www.energyplus.gov> us.gov
<http://www.energypl <http://www.energyplus.gov> us.gov> > us.gov
<http://www.energypl <http://www.energypl <http://www.energyplus.gov> us.gov
<http://www.energypl <http://www.energyplus.gov> us.gov> > us.gov>
<http://www.energypl <http://www.energypl <http://www.energyplus.gov> us.gov
<http://www.energypl <http://www.energyplus.gov> us.gov> > us.gov
<http://www.energypl
<http://www.energypl <http://www.energyplus.gov> us.gov <http://www.energypl
<http://www.energyplus.gov> us.gov> > us.gov> >
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energypl <http://www.energypl <http://www.energyplus.gov>
us.gov
<http://www.energypl <http://www.energyplus.gov> us.gov> > us.gov
<http://www.energypl <http://www.energypl <http://www.energyplus.gov> us.gov
<http://www.energypl <http://www.energyplus.gov> us.gov> > us.gov>
<http://www.energypl <http://www.energypl <http://www.energyplus.gov> us.gov
<http://www.energypl <http://www.energyplus.gov> us.gov> > us.gov
<http://www.energypl
<http://www.energypl <http://www.energyplus.gov> us.gov <http://www.energypl
<http://www.energyplus.gov> us.gov> > us.gov> >
>
> The group web site is:
> http://groups. <http://groups.
<http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/
<http://groups. <http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/> >
yahoo.com/group/EnergyPlus_Support/
<http://groups. <http://groups.
<http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/
<http://groups. <http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/> >
yahoo.com/group/EnergyPlus_Support/>
<http://groups. <http://groups.
<http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/
<http://groups. <http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/> >
yahoo.com/group/EnergyPlus_Support/
<http://groups. <http://groups.
<http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/
<http://groups. <http://groups.yahoo.com/group/EnergyPlus_Support/>
yahoo.com/group/EnergyPlus_Support/> >
yahoo.com/group/EnergyPlus_Support/> >
>
> Attachments are not allowed -- please post any files to the
appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@ <mailto:EnergyPlus-Support%40gard.com> gard.com
<mailto:EnergyPlus-Support%40gard.com>
<mailto:EnergyPlus-Support%40gard.com>
__________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/