[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Cooling a zone without affecting humidity
Hi Justin,
My sincere thanks for your reply.
I'm afraid I cannot alter the AHU in the test. It is necessary to
model the specific compenents themselves and node conditions for
compliance with a standard.
I have reduced the RH levels in the zone to ~40%. However, the cooling
load by the hydronic tubes is never larger than 2.3kW. How can I make
one of these cooling devices as large as possible in order to reduce
zone temperatures from 26C to 21C to offset the air's sensible gain
(air is supplied at 27C).
Kind regards
-Elmer
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Spencer, Justin"
<Justin_Spencer@...> wrote:
>
> Elmer,
>
> If you have any sustained latent loads, then what you are trying to do
> is not possible without separately treating the latent loads. If you
> have no latent cooling capacity, then the humidity will rise until the
> air in the space is fully saturated. At that point, it is impossible to
> do any sensible cooling without also doing latent cooling. So if you're
> not providing enough latent capacity, you won't be able to do any
> sensible cooling.
>
>
>
> It is possible, on the other hand, to set up a separate loop for
> providing latent control, and then have a sensible-only system for
> controlling temperature, the DOAS approach. To do this, you could put a
> dehumidification component into an air loop that provides ventilation
> air to the space (it's possible for this to be latent-only with reheat),
> then use the low temperature radiant hydronic system that Brent pointed
> out to do most of the sensible cooling.
>
>
>
> Justin
>
>
>
> [Non-text portions of this message have been removed]
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/