Re: [EnergyPlus_Support] Night Ventilation Setback
Please review the field definitions in the Input Output Reference (starting on
p. 323, pdf p. 361). For ventilation flow regardless of outdoor and indoor
conditions, the delta temp should be -99, and min temp should be -99. Check
the outdoor temperature and wind speed limits, and also the flow coefficients
should be 1,0,0,0. If this does not fix the problem, please upload the input
file or send as a zipped attachment to energy-plus@xxxxxxxx
Mike
On 3 Nov 2006 at 19:35, elizabeth.ricker wrote:
> Hi,
> I am looking at modeling a single zone "building" that uses simple
> ventilation to supply 4.5m/s during the day and 1.5 m/s of air at
> night to cycle the air in the building. The inside temperature is held
> constant with an electric heater and the outside temperature varies
> for the day of the year (this is a one year simulation). When I try to
> use the simple ventilation input with natural ventilation at 4.5 m/s,
> a minimum temperature of 0, a delta temperature of 0, and a fraction
> schedule that uses 1 for the daytime and .3333 for the nightime I get
> output that is inconsistent. It gives me airflow rates for random
> hours of the day, but not for others, and I can't find a discernable
> pattern between those times when I have air flow and when I dont. Am
> I missing something regarding the ventilation algorithm? Or the
> mechanism for activating ventilation?
>
> Thanks!
>
> -Betsy
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/