[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] For Help! To simulate a skyscraper.
Try modeling representative floors and using multipliers for those, e.g.
Floor 10 *20
Floor 30 *20
Floor 50 *20
Floor 70 *20
well_kong wrote:
> I was assigned to simulate a skyscraper with 80 floors using EP.
> I tried multiplier,but there is a differential load between different
> high floors. For example,there will be about 0.6 C between 20m high.
> And for so many floors,the gap cann't be ignored.
> If I simulated every floors,It's really a huge job especially with a
> HVAC system.And the time of simulation also is a problem.
> Who could help me? Is there any other way to shortcut the work.
>
> Well Kong
>
>
--
*****************************************
Philip Haves
Leader, Commercial Building Systems Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road Bldg 90R3111
Berkeley, CA 94720-8134
Tel: (510) 486 6512
Fax: (510) 486 4089
*****************************************
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/