Re: [EnergyPlus_Support] For Help! To simulate a skyscraper.



One possible suggestion would be to model the building as several blocks 
of floors that use multipliers. So you could have floors 2-19 modeled as 
a single floor with a multuplier, and floors 20-39 modeled as a 
different single floor with a multiplier. The first block could be 
modeled as if it were floor 20, the second block as floor30, etc. The 
number of blocks would be up to you to decide.

I haven't used this technique, but someone from the list should be able 
to confirm that this is possible.

Steven Baker
msbaker@xxxxxxxxxxxxxx

well_kong wrote:

> I was assigned to simulate a skyscraper with 80 floors using EP.
> I tried multiplier,but there is a differential load between different 
> high floors. For example,there will be about 0.6 C between 20m high.
> And for so many floors,the gap cann't be ignored.
> If I simulated every floors,It's really a huge job especially with a 
> HVAC system.And the time of simulation also is a problem.
> Who could help me? Is there any other way to shortcut the work.
> 
> Well Kong 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/