Re: [EnergyPlus_Support] PURCHASED AIR AND VENTILATION
If you want the EnergyPlus simulation to always meet the load, then let the
PURCHASED AIR object have unlimited capacity.
If you want to limit the PURCHASED AIR flow rate, then specify the supply air
flow rate.
Assuming the systems are balanced such that the outdoor air flow is equal to or
greater than the exhaust fan flow, then specify the outdoor air flow rate in
the VENTILATION object(s).
If you are modeling three thermal zones to align with the 3 air handlers, then
you may also want to add a MIXING object if there is a net flow of outdoor air
from the dining area(s) into the kitchen.
All of this assumes that the air handlers will be constant volume with
continuous fan during occupied hours.
Mike
On 10 Nov 2006 at 14:38, lbdm_linda wrote:
> Hi!, my name is Lorena, I'm learning EnergyPLus, I'm modeling a
> restaurant which has 3 air handling units and some exhaust fans in the
> kitchen. I want to use the PURCHASED AIR object, and I have
> information on the building's Outdoor air, supply air, return air and
> the Kitchen's exhaust air. Where should I specify each one of those,
> which flow rate should I specify for the Ventilation object?
>
> Thanks in advance!.
>
> Lorena.-
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/