Re: [EnergyPlus_Support] Other side coefficient
It all depends on what you are trying to answer in your simulation. If the
surrounding spaces are similar to the classrom you want to model and are
conditioned to the same temperatures, then you may want to make the interior
surfaces adiabatic. For example Surface:HeatTransfer, Name=Wall1,
OutsideFaceEnviornment=OtherZoneSurface, OutsideFace Environment Object=Wall1.
Or you can model the surrounding spaces in their entirety as separate thermal
zones if the conditions in those zones will be significantly different.
Mike
On 16 Nov 2006 at 10:59, David Barrera wrote:
> Dear all:
> I need to simulate a room, tne thing is that it's
> located among three other classrooms (on the top, left
> and right) and I thought in defining air temperatures
> for those other rooms, in order to stablish exterior
> conditions for those walls conected to the other
> rooms. The only thing is that, as you already know,
> not only air temperature is requiered in this section
> but also many other complex parameters such as combine
> convective/radiative film coefficient. Do I have to
> difine all of them, just some of them, or what can I
> do?
> Thanks a lot.
>
>
>
> ______________________________________________________________________________
> ______
> Sponsored Link
>
> Mortgage rates near 39yr lows.
> $420k for $1,399/mo. Calculate new payment!
> www.LowerMyBills.com/lre
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/