Re: [EnergyPlus_Support] Psychrometric Error
If you use performance curves from an example file (such as
FurnaceWithDXSystem.idf) does the simulation run without such errors?
If so, the problem is probably in the curve fits. Have you taken the curve
fits and plotted them against a range of temperature conditions to see if the
shapes are reasonable?
Mike
On 21 Nov 2006 at 2:03, eric_zhou1223 wrote:
> Hi£¬
>
> I am trying to replace the performance curves of
> Coil:DX:CoolingbypassFactorEmpirical
> with some fitted curves from a manufacturer catlogue. The simulation run well
> but poped
> out some errors. Does it mean that E+ thought the coil is giving impossible
> capacity? What
> shall I do to fix it?
>
> Thank you in advance.
>
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Enthalpy=-71700.29 Pressure= 101900.0
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -89563.99
> ** ~~~ ** Calculated Humidity Ratio= -1.2255E-02 ... Humidity Ratio set
> to .00001
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Enthalpy=-60525.36 Pressure= 101900.0
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -78389.05
> ** ~~~ ** Calculated Humidity Ratio= -7.5789E-03 ... Humidity Ratio set
> to .00001
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Enthalpy=-53785.87 Pressure= 101900.0
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -71649.57
> ** ~~~ ** Calculated Humidity Ratio= -4.7583E-03 ... Humidity Ratio set
> to .00001
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Enthalpy=-53318.36 Pressure= 101900.0
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -71182.06
> ** ~~~ ** Calculated Humidity Ratio= -4.5626E-03 ... Humidity Ratio set
> to .00001
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Enthalpy=-53570.60 Pressure= 101900.0
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -71434.30
> ** ~~~ ** Calculated Humidity Ratio= -4.6682E-03 ... Humidity Ratio set
> to .00001
> ** Warning ** Enthalpy out of range (PsyTsatFnHPb)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Enthalpy=-53564.07 Pressure= 101900.0
> ** ~~~ ** Initial Resultant Temperature= -59.98
> ** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/01 07:30 - 08:00
> ** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -71427.77
> ** ~~~ ** Calculated Humidity Ratio= -4.6655E-03 ... Humidity Ratio set
> to .00001
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/11 07:30 - 08:00
> ** ~~~ ** Input Temperature=-213.43
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/11 07:30 - 08:00
> ** ~~~ ** Input Temperature=-213.90
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/11 07:30 - 08:00
> ** ~~~ ** Input Temperature=-136.06
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/11 07:30 - 08:00
> ** ~~~ ** Input Temperature=-136.29
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/11 07:30 - 08:00
> ** ~~~ ** Input Temperature=-136.06
> ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
> ** ~~~ ** Occurrence info=NEW_YORK_CITY NY USA TMY2-94728
> WMO#=744860, 08/11 07:30 - 08:00
> ** ~~~ ** Input Temperature=-136.29
> ************* Psychrometric Error Summary
> ************* Routine - Number of errors
> ************* PsyTdpFnTdbTwbPb-0
> ************* PsyRhFnTdbWPb-0
> ************* PsyTwbFnTdbWPb-0
> ************* PsyVFnTdbWPb-0
> ************* PsyWFnTdpPb-0
> ************* PsyWFnTdbH-124228
> ************* PsyWFnTdbTwbPb-0
> ************* PsyWFnTdbRhPb-0
> ************* PsyPsatFnTemp-14996
> ************* PsyTsatFnHPb-154530
> ************* PsyTsatFnPb-0
> ************* tp12c0-0
> ************* tp12c1-0
> ************* tp12h0-0
> ************* tp12h1-0
> ************* freeze-0
> ************* EnergyPlus Completed Successfully-
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/